Discuss Running PME (TNCS) outdoors? in the Australia area at ElectriciansForums.net
read the 17th edition, nickname ( the bumper book of fun ) pme or tn-c-s supports neutral, connot run live connductor outside of building, best way is run phase & neutral, to garage,
and put earth stake in for protection, only to garage consumer unit though, bit like a builders supply realy, but thats the reg's
i could explain in detail, but would take a long time
Where is this regulation? It has obviously been omitted from my copy of BS7671:2008 with corrigendum.
The only one I can recall is a PME supply shall not be run INSIDE a domestic premises.
That reg refers to PEN conductors and is not restricted to domestic installations.
The PEN conductor only goes as far as the service head where it is separated!
1. Apart from some special locations as defined in section 7 of bs 7671 there are no regulations in bs 7671 preventing a TNCS (PME) supply being used to supply external equipment and outbuildings.
2. The DNO dont give a ---- about exporting TNCS supplies as long as it complies with Bs 7671.
3. The reason regulations on exporting PME earths or separating for external supplies which are not a special location cant be found in the BRB is because they are not in there.
END OF.
END OF.
Ah, a pleasure to read......
lol wirepuller you REALLY hate this subject dont you.
Not as much as me, people just manufacture 'reg's based on rumour and opinion, it's pretty basic stuff in the scheme of things!
Guys use these threads to assist in their studies etc. so let's not make up regulations!
The impression I get is that the presence of extraneous conductive parts does not preclude the use of an exported TNC-S earth, it mearly means that they have to be bonded back to the submain MET with the same size cable as is appropiate for doing the same in the main building, and that the same sized or bigger earthing cable is used to provide the earth to the submain board, and as this is not always practical, a way of avoiding having to install bigger cables is to convert the remote installation to TT, and bond extraneous bits back to this
I think!!!!!!
pretty much what i think too :) -and once you get to about 12M of 10mm bonding it gets cheaper to to put an earth electrode in unless there is some other complicating problem.
Reply to Running PME (TNCS) outdoors? in the Australia area at ElectriciansForums.net
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Hello, I'm new to this forum, we are in the process of converting into 12 flats all electric, no gas incl. heating, showers etc. An electrician...
Hi guys I have a question on installing an outside supply to a spa at home. I have a few questions regarding this one is the consumer unit has no...
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
5K