I have a s/phase submersible pump, remote float sw control, (capacitor run 20uF, capacitor start 100uF,) app 20years of age, 2in bore drawing around 6A when running on load. It has developed a problem on start up which i believe i have diagnosed and indicates that the capacitor start up relay (only 3 connections), is the culprit.

It will start after the 2nd of 3rd attempt and then run fine continuously (the capacitors test out O.K. with a capacitor meter). I am having great difficulty in sourcing a replacement relay, having tried Remco capacitors, RS, Farnell, and a pump spares company, if anyone could help with any information i should be most grateful.
thank you Griffey.
 
what's the chance of a pic of the relay?
 
Have you checked the centrifugal switch is operating at the right time / speed?
 
Pete I think it's like a fridge compressor start relay. The relay coil is in series with the run winding and the contacts are in series with the start winding. At standstill the heavy current through the run winding operates the relay energising the start winding. Once the motor is up to speed the current drops and the relay opens the start circuit. They are used where it's difficult to fit a centrifugal switch on motors driving fairly predictable loads.

OP beware the capacitor meter as a test device. Failing electrolytic caps can sometimes measure OK for capacitance, but break down under mains voltage. However, these relays are not massively reliable and are considered a replaceable part, so your diagnosis may well be correct. I would not be surprised if the relay on your pump also has a refrigeration application so you might try that avenue.
 
Pete I think it's like a fridge compressor start relay. The relay coil is in series with the run winding and the contacts are in series with the start winding. At standstill the heavy current through the run winding operates the relay energising the start winding. Once the motor is up to speed the current drops and the relay opens the start circuit. They are used where it's difficult to fit a centrifugal switch on motors driving fairly predictable loads.

OP beware the capacitor meter as a test device. Failing electrolytic caps can sometimes measure OK for capacitance, but break down under mains voltage. However, these relays are not massively reliable and are considered a replaceable part, so your diagnosis may well be correct. I would not be surprised if the relay on your pump also has a refrigeration application so you might try that avenue.
Thanks Lucien
 
Pete I think it's like a fridge compressor start relay. The relay coil is in series with the run winding and the contacts are in series with the start winding. At standstill the heavy current through the run winding operates the relay energising the start winding. Once the motor is up to speed the current drops and the relay opens the start circuit. They are used where it's difficult to fit a centrifugal switch on motors driving fairly predictable loads.

OP beware the capacitor meter as a test device. Failing electrolytic caps can sometimes measure OK for capacitance, but break down under mains voltage. However, these relays are not massively reliable and are considered a replaceable part, so your diagnosis may well be correct. I would not be surprised if the relay on your pump also has a refrigeration application so you might try that avenue.

Hi thank you for your comments and the information, i think i shall fit a timer and power relay to switch the start capacitor. Thank you.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
staffordshire
What type of forum member are you?
Retired Electrician

Thread Information

Title
S/phase submersible pump starting problem.
Prefix
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
14

Thread Tags

Advert

Thread statistics

Created
Griffey,
Last reply from
Griffey,
Replies
14
Views
1,465

Advert

Back
Top