Double pole switching, that is. I.e. SP + N.
DP is for split phase.
 
£650 is an extremely good price in my opinion especially if your electricians work is good. A full day seems about right too. In all honesty there couldn’t be a huge amount of circuits as 650 wouldn’t cover more then 6/7 circuits if I was doing it. If you are happy with his work, I’d say you should go with it.
 
Don't think I've ever come across a DP RCBO, but a DP MCB has a current sensing element in each pole, and usually consists of two SP MCBs rivetted together with a link between the toggles. A SP & N MCB has a current sensing element in the live pole and just a switch in the neutral.
If the RCBO in question was used on a split phase supply, the RCD element would still work on both poles (unless there was an equal leak to earth on each phase), but one of the phases would not have any overload or short circuit protection.
 
Don't think I've ever come across a DP RCBO, but a DP MCB has a current sensing element in each pole, and usually consists of two SP MCBs rivetted together with a link between the toggles. A SP & N MCB has a current sensing element in the live pole and just a switch in the neutral.
If the RCBO in question was used on a split phase supply, the RCD element would still work on both poles (unless there was an equal leak to earth on each phase), but one of the phases would not have any overload or short circuit protection.

I remember a discussion from some time back, in which it was discovered that certain 'DP' (2 module) RCBOs were also SPSN.
 
To be honest we probably aren't doing a lot to help the OP ask a clear question of his electrician!
The point is that when you turn the thing off (or it trips) both Line and Neutral are broken so the circuit is completely isolated and any faults can't cause issues elsewhere. While the learned people are right, to be honest "double pole" is probably the term that is most likely to be instantly understood by the average domestic sparks.
CEF call the Lewden RCBOs "single pole" vs "single pole and neutral", the latter being the one's that would be best to use.

(to add to the confusion Fusebox SPN units do not break the Neutral and they call the one's that do DP ....!)
 
Don't think I've ever come across a DP RCBO, but a DP MCB has a current sensing element in each pole, and usually consists of two SP MCBs rivetted together with a link between the toggles. A SP & N MCB has a current sensing element in the live pole and just a switch in the neutral.
If the RCBO in question was used on a split phase supply, the RCD element would still work on both poles (unless there was an equal leak to earth on each phase), but one of the phases would not have any overload or short circuit protection.


Electronic type
• Residual current characteristic: AC
• No of poles: 2 (L and N)
• Trip curves: B and C
• Rated voltage: 240V AC, 50/60Hz
• Short circuit capacity: 10kA
• Rated current (A): 6, 10, 16, 20, 25, 32, 40, 50, 63
• Rated residual operating current, In (mA): 30
• Electrical endurance: 4000 cycles
• Mechanical endurance: 10000 cycles
• Conforms to: IEC/EN 610009-1
 