Hi, I live in a victorian terrace in Walthamstow and had an ask from the landlord next door for an electrician to fit a shared earth. I electrics 2.jpgelectics 3.jpgquestioned this so on a call the landlords electrician explained that we have a terra neutral combined separate supply. The main supply comes into my house under the stairs then splits to next door. They want to do a test and see if earthing is satisfactory and come off our main earth terminal (as far as I understand this is the main box in the picture). Online advice is that this isnt recommended, but fully qualified and experienced landlords electrician said this is perfectly normal for the type of supply we have. Pictures attached - I am planning no work my self, just advice to see if this is ok before they come in to do the work!
Next door does appear to take their supply from the service head at your property. The only earthing conductor from the service head would appear to just serve your property, it should be noted that earthing connection to the service cable is non compliant and I suspect it maybe an adhoc earthing arrangement. The service head it much more recent than the service cable which is a great deal older so I wonder if an earth was refused by the DNO when the head was replaced as the obvious thing to do was give you a TN-C-S earth. Makes me wonder what at present is earthing the adjacent property as those supply conductors going through the wall are probably the same age as the supply cable.
Thanks for the response. As far as I understand it the need for the work is because next door currently lack an earth at all and need to earth through mine. According to the text: "by taking a cable from the silver earth block through the wall into their property"
Hi, I live in a victorian terrace in Walthamstow and had an ask from the landlord next door for an electrician to fit a shared earth. I View attachment 125109View attachment 125110questioned this so on a call the landlords electrician explained that we have a terra neutral combined separate supply. The main supply comes into my house under the stairs then splits to next door. They want to do a test and see if earthing is satisfactory and come off our main earth terminal (as far as I understand this is the main box in the picture). Online advice is that this isnt recommended, but fully qualified and experienced landlords electrician said this is perfectly normal for the type of supply we have. Pictures attached - I am planning no work my self, just advice to see if this is ok before they come in to do the work!
Where do the meter tails (L2 + N) go to underneath the meter board.
There does seem to be an earthing conductor passing through with them?
A shared earth is not something that is common!
L3 appears to serve your property?
You also do not have a 'silver' earthing block but no big deal to install one.
You might want to upgrade the earthing clamp whilst sorting the neighbour out as it is a pipe clamp, not suitable for lead sheathed cables.
I think that conductor just loops behind the tails which go through the wall.
As Westward said that is a non compliant earthing arrangement. You need to contact the DNO to enquire about that and this seems a good opportunity to bring up the conversation about your shared supply set up. Probably some historical reasons for this.
It would cause a disruption to your neighbour but worth exploring the possibility of them getting their own supply installed hopefully at no cost to them.