If you test continuity of a lighting circuit neutral to the block surely you should get continuity?!!

If I know there are two circuits then one way is to IR between the Neutrals of each circuit from the roses or pendants but that needs to be done in daylight with power off , in my experience it usually happens in the two way between hall & landing lights
 
Sorry, not very well explained. Disconnect the first floor lighting neutral at the board, then check for continuity between the end of the disconnected neutral and the block. It won't tell you where the neutral is borrowed from, just if there is one. Two minute job, all at the board, only lights off on one floor.
 