stokecity
Hi guys, im putting electric into my shed, total distance from house cu to shed cu is 18 Meters how does this sound.
25a mcb at supply end on RCD side
4mm armoured 3core buried
shed cu with 20a radial with 2 double sockets
6a for light.
Will have around 3 kw running at 1 time probably less.
Got 2 sparks 1 says this will be fine other says up to 6mm SWA . Don't want to spend the extra on the 6mm if its just been over cautious. What do you guys think
25a mcb at supply end on RCD side
4mm armoured 3core buried
shed cu with 20a radial with 2 double sockets
6a for light.
Will have around 3 kw running at 1 time probably less.
Got 2 sparks 1 says this will be fine other says up to 6mm SWA . Don't want to spend the extra on the 6mm if its just been over cautious. What do you guys think