Hi Mark ... neat job and only minor notes from me..
-You have singles entering the board and seem to have ID'd the L & N but your earthing is not it would seem, any following Electrician is going to need to follow the earthing to the jungle of SWA glands to confirm.
-As noted above cut all the ties in the trunking to allow dissipation of heat.
-Also hard to tell but swa grouping should be no more than 3 per group to allow good heat dissipation ...you may have already done this but its hard to tell as I said.
-Lastly I don't see any main earthing link to the bottom power switch section, these boards are only slotted and tapped together with a few screws, you should not rely on this to make an effective earth route.
Other than my minor comments, I commend you on a neat job.