Discuss Shower circuit tripping in the UK Electrical Forum area at ElectriciansForums.net

Does it trip if the line conductor is removed from the MCB?

Has the MCB been weakened by someone repeatedly closing it on to a fault (which may no longer be there)?

What was the initial failure? Has the customer had a faulty shower which has been replaced but caused damage to the MCB?

Welcome to the forum by the way.
 
Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
 
Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
Mcb on order only changed cable as easy swap and showed signs on damage and stripped to far back not long enough to re terminate.is there a way to test mcb is faulty?
 

Reply to Shower circuit tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
733
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
424
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock