Shower circuit (40a mcb 10mm cable 8.5kw shower ) tripping after 5 mins RESET trips after 2 mins...changed shower /cable /isolator still tripping I'm stumped
 
Does it trip if the line conductor is removed from the MCB?

Has the MCB been weakened by someone repeatedly closing it on to a fault (which may no longer be there)?

What was the initial failure? Has the customer had a faulty shower which has been replaced but caused damage to the MCB?

Welcome to the forum by the way.
 
Randomly replacing parts without knowing the cause is not the way forward and is costing money. What tests have you done?
 
Drawing 34.7a when in use
Changed cable as cu to isolator was simple and only 2m away cable to shower was only 6mm again easy change. IR on cable disconnected from shower ⁹>999
 
Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
 
  • Like
Reactions: nicebutdim and DPG
Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
Mcb on order only changed cable as easy swap and showed signs on damage and stripped to far back not long enough to re terminate.is there a way to test mcb is faulty?
 
Put a clamp meter on the outgoing cable, if it is tripping before it’s rated output, it has had its day.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Neath, Neath Port Talbot
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Livewire electrical

Thread Information

Title
Shower circuit tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Scott 12345,
Last reply from
James,
Replies
7
Views
951

Advert