Shower circuit (40a mcb 10mm cable 8.5kw shower ) tripping after 5 mins RESET trips after 2 mins...changed shower /cable /isolator still tripping I'm stumped
 
Does it trip if the line conductor is removed from the MCB?

Has the MCB been weakened by someone repeatedly closing it on to a fault (which may no longer be there)?

What was the initial failure? Has the customer had a faulty shower which has been replaced but caused damage to the MCB?

Welcome to the forum by the way.
 
Drawing 34.7a when in use
Changed cable as cu to isolator was simple and only 2m away cable to shower was only 6mm again easy change. IR on cable disconnected from shower ⁹>999
 
Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
 
Cable change was probably not required
if the current is constantly below 40A then a faulty breaker is likely, assuming it is just an Mcb.
if it is an rcbo then of course there could be other root causes.
Mcb on order only changed cable as easy swap and showed signs on damage and stripped to far back not long enough to re terminate.is there a way to test mcb is faulty?
 