hold on....he`s only got 63A to play with on the existing CU.....up the RCD to 80A....or put an add on board for shower....
make sure tails etc are up for extra load....

He wont have a problem, the shower wont be on long enough for it to blow the fuse, unless he leaves it running for a fortnight when he goes away on holiday.

I have fit loads of showers with an assumed 60a main cutout fuse, i say assumed, because we dont remove them do we:smilewinkgrin: to find out. His shower is only going to pull 36 amps assuming it is on maximum hot, diversity and so on, he will be fine.

my concern is the Part P thing.

Cheers..........Howard
 