Isn't the recess classed as zone 2? Should have mounted it in there.
Thank you for corrections on that mate, I'm in my first year learning so using the forum as a tool etc very clumsy bit of advice with this one but I might remember my zones next time right hahaShower enclosure is zone 1, and "certain IP rating" is required, but conditions inside the shower enclosure are not uniform. The nearer to the bottom you go, the greater the chance is that the equipment will be subjected to spray (needs IPX5), rather than just subject to splashing from all directions if mounted higher up (IPX4).
IMHO, this shower is mounted so that it could receive a direct spray from the shower head, and IPX4 is not adequate.
Dont know how you can ever ensure that with a flexible shower hose other than trying to educating the users! and stick with my comments in post#15"10. The showerhead must be directed away from the shower unit, during normal
use the showerhead must not spray directly on to the shower unit."
The point being made here is that the water is intended to be in the same axis as the unit, ie side by side, not adjacent.Dont know how you can ever ensure that with a flexible shower hose other than trying to educating the users! and stick with my comments in post#15
Last remote mounted shower I came across was mounted on a piece of chipboard in the well ventilated loft, above the 200mm of insulation, just waiting for a nice low temperature winter's night. Even the copper pipework to it was exposed.Digital mixers / Smart valves are the way to go, taking the unit out of zone 1 completely.