Shower enclosure is zone 1, and "certain IP rating" is required, but conditions inside the shower enclosure are not uniform. The nearer to the bottom you go, the greater the chance is that the equipment will be subjected to spray (needs IPX5), rather than just subject to splashing from all directions if mounted higher up (IPX4).
IMHO, this shower is mounted so that it could receive a direct spray from the shower head, and IPX4 is not adequate.
Thank you for corrections on that mate, I'm in my first year learning so using the forum as a tool etc very clumsy bit of advice with this one but I might remember my zones next time right haha
 
Lifted straight from the Installation guide, took me 10secs on Google....

"10. The showerhead must be directed away from the shower unit, during normal
use the showerhead must not spray directly on to the shower unit."

So it's not been fitted in accordance with the manufacturers instructions, get the electrician back to correct it, and they're also going to have to fork out for all the corrective decorative work too, so it's likely an insurance claim.

 
That being said...... which came first - the cable or the pipe?! There's possibly a plumber to blame here as well, in which case it could get messy.
 
"10. The showerhead must be directed away from the shower unit, during normal
use the showerhead must not spray directly on to the shower unit."
Dont know how you can ever ensure that with a flexible shower hose other than trying to educating the users! and stick with my comments in post#15
 
Dont know how you can ever ensure that with a flexible shower hose other than trying to educating the users! and stick with my comments in post#15
The point being made here is that the water is intended to be in the same axis as the unit, ie side by side, not adjacent.
 
Arguably it's the riser rail that's in the wrong place.
If the riser rail was on the same wall as the unit it wouldn't be pointed right at the unit in normal use.
I have to say though that I have never yet seen an issue with water ingress into a mira sport even when installed like that.
 
I replaced a Mira shower unit a few weeks ago where the client had fitted a turbo power head which worked fine, but it had a stop valve at the head.

Ended up with the tank bursting, gushing water into the enclosure.

Digital mixers / Smart valves are the way to go, taking the unit out of zone 1 completely.
 
Digital mixers / Smart valves are the way to go, taking the unit out of zone 1 completely.
Last remote mounted shower I came across was mounted on a piece of chipboard in the well ventilated loft, above the 200mm of insulation, just waiting for a nice low temperature winter's night. Even the copper pipework to it was exposed.
I was only there for an EICR, although I did pass my thoughts onto the landlord.
 