nickblake
No No and No , any thing above 3 kw should be on its own circuit so adding anything to it would be a crontravention of the regs , showers can be a right pain especially the isolator if you have a 10mm cable there is in no way you should have another cable installed in there fused or not fused its poor workman ship , if i was going to add a light in the shower cubicle then i would install a PIR as telex has said and connect to the light you walk in the light come on , i have had experiance with other appliances connected to shower IE extract fans wire from the shower connections and yes £15,000 for a new roof after the loft caught fire due to the cable si9lly in my eye's