You could put a RCBO in at the DB though? what make of Dist board have you got? Make sure a spark Does it though.

It's an old Wylex plug in fuse type, fitted in the mid 80's...could do with being updated really to be honest as it would probably be overloaded with everything switched on. It would probably be more reasonable to replace it, but access is tight.

Cheers
 
I know the answer I have put in at least 20 posts relating to showers already yes they do.
Section 134 ERECTION AND INITIAL VERIFICATION OF ELECTRICAL INSTALLATIONS
134.1 Erection

Regulation 134.1.1Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation, Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment.

PART 5 SELECTION AND ERECTION OF EQUIPMENT
CHAPTER 51 COMMON RULES
510.3
Every item of equipment shall shall be selected and erected so as to allow compliance with the regulations stated in this chapter and the relevant regulations in other parts of BS7671 and shall take account of manufacturers' instructions.
 
Why not get an electrician in? Then you don't have to take that risk of electrocution.

The last time I had an electrician in, he supposedly bonded my bathroom radiator, only I later found out that he had simply clamped the wire to my radiator and pushed the other end under the floorboard, left disconnected. I'm sure not every electrician is like that, but I have always gone with...if you want something doing right...do it yourself...but there are times when it's unavoidable. I genuinely do try to avoid having any workmen in my home, because I don't trust no one...and I'm tight!!!
 
7671 is telling you to use manufactures instructions even they are telling you that, so I can't see why you don't agree with me?
 
No it says the manufacturers' instructions should be taken account of.
That does not mean the instructions have to be followed.
 
If you didn't follow the instructions and something happened what would you be prosecuted with?
 
Not meaning to jump in an argument, nor do i want grief at this time of night but...

If you didn't follow the instructions and something happened what would you be prosecuted with?

In a court of law, you've got to provide evidence you've done the job correctly and safely...if you've complied with BS7671 (regardless of the manufactures instructions), then this is adequate IMO!

Can see both points though, agree to disagree fella's :)
 
Given the garbage that is passed off as English language by a lot of manufacturers
It would be nigh on impossible to follow their instructions,that is without first engaging the services of some Norwegian dyslexic to translate it into something meaningful
 