P

pcam1984

Hi guys, been asked to change a shower, customer wants to put a 9.5kw in place of 8.5kw. Supply is db to dp sw 6mm t+e (7m) then sw to shower 10mm t+e (7m). I was thinking 6mm should be upgraded to 10mm but customer doesnt want the mess! What do you guys think?
 
what reference method for the 6.0mm? if it's method C then you're OK. if covered in insulation crap, then either move the crap or upgrade cable to 10mm.
 
Tell them they are Scottish and lot to be whimps and stick with a 8.5kW... Problem solved...
 
The 6mm is clipped under a floor but no insulation but it drops down to the db bunched with other cables. Its one of those ones that its borderline, the cable can take take it but id still prefer it to be 10mm
 
not if you put it on a 32A MCB.
 
not if you put it on a 32A MCB.

Assuming its not already, and changing the protective device means a new EIC.

pcam, a 9.5kw shower is what its been rated at 240v, at nominal voltage (230v) its 8.7kw check the box. so thats pretty much like for like, advise cable is upgraded before they put a 10.5 in next time.......looks like they are heading that way.
 
it's nominally 39.5A. bet if you clamp it , it won't pull more than 35A.
 
Using a 6mm T+E cable, bunched with other cables, and/or running it on a 32Amp CB are both bad design practices, and almost certainly will not comply with the Regs.

Separate the cable from the others, and it may then comply, but not on a 32A CB, use a 45 or 50A.
 
BGB Table 4D5 Method C 47Amps.

Using a 6mm T+E cable, bunched with other cables, and/or running it on a 32Amp CB are both bad design practices, and almost certainly will not comply with the Regs.

Separate the cable from the others, and it may then comply, but not on a 32A CB, use a 45 or 50A.
 
433.3.1 (ii) will apply to an electric shower,if it has fault protection, hence no need for overcurrent protection.
 
now, that is a get out of jail free card. complies with regs., but is it good practice?
 