Hi all
I've been asked to put in a shower needing a 40 amp breaker but there is only a 30 rcd on the 1 half of the board what is the easiest way of doing this as a freind of mine sid that as long as you have a disconection of .5 secs you dont need to but i cant find anything to confirm this. is this correct or is he quoting something that was ok in the past?
Please help me clear this up
Tom:confused:
 
The shower needs to be RCD protected if it's going in the bathroom,i assume it's going in the bathroom.What are you asking mate:confused:
 
it is going in the bathroom but a friend of mine said it does not have to be if it has a short disconection time but i could not find this anywhere and i just wanted to clear the confusion up
 
if there is no space on the rcd protected side of the board you would need to split the tails at incoming and put in a 3 way board, 30ma rcd, 40a breaker for shower and 6a for the lighting circuit that would include the bathroom light to comply with 17th edition. =0)
 
there is space on the rcd side but in the osg it has a 30ma rcd to cover circuits not exceeding 32a and i need to put in a 40a
 
there is space on the rcd side but in the osg it has a 30ma rcd to cover circuits not exceeding 32a and i need to put in a 40a
all curciuts in a room containing a bath/shower p 69 on site guide all curcuits to be protected by 30ma rcd
 
ok read that but why on p.24 does it say circuits not exceeding32a

thats for anywhere eles other than a special location a shower room is a special location

old regs was ok for shower not to be rcd protected but not now

hope this helps
 
Protection
All electrical circuits within bathrooms must be protected by Residual Current Devices (RCD) not excedding 30mA. This applies all electical equipment whether it is controlled a switch in the bathroom or remotely switched.
Equipment for bathrooms
Electrical equipment may be identified as having a certain level of mechanical and moisture protection, these are quoted as 'Ingress Protection' (or IP) numbers - such as 'IPXY', where X and Y are numbers, the X showing the level of mechanical protection and Y showing the level of moisture protection - in both cases, the higher the number, the better the protection. If a piece of equipment does not have an IP number, it must not be used in zones 0, 1 or 2 (or elsewhere having a wet/damp environment
 
I think its only distribution circuits over 32A do not need RCD protection.

This assumes that the cable installation method would not need it.
 