Welshsparky

Fitted a socket for a customer today, Job done.... 2 hours later call from the customer " All my power is off" turns out to be the rcd tripping, Went back checked the socket and all was fine, checked the rcd with the socket unscrewed from the wall and no problems, screwed the socket back and rcd trips... no sign off damage to any conductors ... any ideas?
 
bet you any money the neutral is catching the earthed back box if the neutal slips behing the screw terminal when its screwed up can short out the screw to the neutral or just clip it it can be very hard to see as the damage can be like a very fine cut it will be the neutral as the live would go bang, im sure youll find neutral to earth is the problem
 
agree. either that or there is a nick in insulation and cable squashed against back box.
 
I have had a problem like this, the problem is not with the socket that you screw back, for me the problem was with the leg of the ring connected to that socket, its hard to explain.
But try IR testing the cables with the legs split
 
Might be simpler than that. check polarity of the socket.

highly unlikely that polarity would cause this.
The main culprit is often the fixing screw, the ideal type of screw is round head or pan head. Countersunk screws stick out leaving a sharp bit all round just waiting to snag one of the conductors
 
highly unlikely that polarity would cause this.
The main culprit is often the fixing screw, the ideal type of screw is round head or pan head. Countersunk screws stick out leaving a sharp bit all round just waiting to snag one of the conductors
Afraid i had just this, neutral and earth were reversed, painter took one off to do some work and left hanging off, as soon as he screwed back and touched the backbox with screw, click.
 
Afraid i had just this, neutral and earth were reversed, painter took one off to do some work and left hanging off, as soon as he screwed back and touched the backbox with screw, click.
Yep seen that, also wired one up reverse myself once when the socket looked identical to the rest but obviously wasn,t and l and n were opposite way round at back.spotted it straight away on test though so luckily no harm done.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Socket screwed back trips rcd...
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
Welshsparky,
Last reply from
mark ju,
Replies
13
Views
11,425

Advert

Back
Top