Discuss Soil earth resistance survey in the UK Electrical Forum area at ElectriciansForums.net

pc1966

Esteemed
Arms
Reaction score
11,932
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area of 150 x 40m or so with possible need for lightning protection and/or input to the decision to have the substation within the site or far enough out that hot/cold separation of LV/HV earths is possible.

I was thinking of getting the Megger DET4TCR2 and their ETK100 probe kit (though a bit galling how much they charge for a few reels of wire and some spikes!) if this is likely to happen as we would need it at a few stages: design, initial testing, and then on-going checks on earth electrode impedance, so longer term its probably better than hiring. But have no experience of those 4-electrode testers to know the good, the bad, and the ugly.

TL;DR any helpful suggestions on measuring soil impedance profiles?
 
I used 9mm earth rods with a right angle bend on the top and earth wander leads suitably sleeved to denote the different positions, worked out a lot cheaper: 9mm x 1200mm Earth Rod (3/8" x 4ft) - https://www.tlc-direct.co.uk/Products/TLER.html the unit was a PeakTech 2700 only a three probe unit though: «PeakTech® P 2700» Digital earth tester, 0-2000Ω, CAT III 1000V | P 2700 - https://www.peaktech.de/uk/PeakTech-P-2700-Digital-earth-tester-0-2000O-CAT-III-1000V/P-2700 I still have it, but no use to me anymore, may be of some help to you if you need it.
 

Reply to Soil earth resistance survey in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i don't the exact value of the soil resistivity as no survey of soil sample is carried out at the site .However Copper earthing electrode 50mm...
Replies
5
Views
1K
Here is my dilemma. Picture this arrangement: a system with a 100A three-phase supply will have a RCD incomer (and possible some generator...
Replies
9
Views
7K
Is anyone able to clarify with me how i can work out what earthing arrangement i have on site. Supply comes into one of our motor switch rooms...
Replies
5
Views
2K
A
Good evening!! i have recently been looking into earth electrode systems, which got me onto reading BS 7430:2011. I am hoping that someone on...
Replies
1
Views
4K
Engineer54
E
T
Pipe in Cage Technology having Electrolytic Earthing System is a multipurpose Earthing system. It has been designed to provide long...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock