Went to see the 72-year-old Dad of a teacher at the school because his electric has been tripping. Get there to be told he's had issues with it since he moved in six years ago but it's getting progressively worse.
TT system, single RCD for the whole board, so when it trips it takes the lot. So I get to testing IR on the board, both L-E and N-E readings are kicking about 2-3Mohms. I tested globally first, then starting to test individually each circuit in the hope of finding a single fault. Every circuit except the shower circuit was reading 2-3Mohms L-E and N-E. The shower tested >200, so I can only assume it was a newer install, especially since it's MCB didn't match the rest of the board make/model wise.
So by now I'm at the conclusion that there's a general breakdown of the insulation of the whole install. I fire it all back up and clamp the earth - it was ticking over at 10mA constant but peaked at around 20mA for a brief second a couple of times. While clamped I turned MCBs off one at a time to see what impact each circuit had, and they all contributed in some way or another.
So hopefully after reading this, you're at the same conclusion as me - rewire needed.
However, that's where it gets tricky. The guy is 72, is in ill health (meningitis, recent stroke and heart attack, brain tumour, blind in one eye - basically a ticking time bomb), and he's not sure what to do. I suggested perhaps it could prolong the inevitable to change the board to DP RCBOs so that there's less current for each device - hopefully stopping tripping, or at least if it does trip it'll be isolated to one circuit and won't be without all electricity.
So I need some advice. I said it needs a rewire ideally, but don't want to push him down that path when he could be dead tomorrow - it's a lot of money as well as disruption for someone of such ill health. What would you do:
TT system, single RCD for the whole board, so when it trips it takes the lot. So I get to testing IR on the board, both L-E and N-E readings are kicking about 2-3Mohms. I tested globally first, then starting to test individually each circuit in the hope of finding a single fault. Every circuit except the shower circuit was reading 2-3Mohms L-E and N-E. The shower tested >200, so I can only assume it was a newer install, especially since it's MCB didn't match the rest of the board make/model wise.
So by now I'm at the conclusion that there's a general breakdown of the insulation of the whole install. I fire it all back up and clamp the earth - it was ticking over at 10mA constant but peaked at around 20mA for a brief second a couple of times. While clamped I turned MCBs off one at a time to see what impact each circuit had, and they all contributed in some way or another.
So hopefully after reading this, you're at the same conclusion as me - rewire needed.
However, that's where it gets tricky. The guy is 72, is in ill health (meningitis, recent stroke and heart attack, brain tumour, blind in one eye - basically a ticking time bomb), and he's not sure what to do. I suggested perhaps it could prolong the inevitable to change the board to DP RCBOs so that there's less current for each device - hopefully stopping tripping, or at least if it does trip it'll be isolated to one circuit and won't be without all electricity.
So I need some advice. I said it needs a rewire ideally, but don't want to push him down that path when he could be dead tomorrow - it's a lot of money as well as disruption for someone of such ill health. What would you do:
- Only accept a rewire, walk away if not
- Happily change the board in the hope it gets a little more life from the aging wiring
- Something else