A customer has had a mare with their kitchen install which one of our Eastern European friends working for a builder who's since gone bust did, you know the scene.
The pic attached isn't great so I'll try and explain what's what & any advice on how to sort it would be appreciated.
The first way from the RCD on left is 40a with the 6mm cooker circuit & the 2.5mm kitchen sockets in.
Then there's a couple of 2.5mm RFC's (brown) followed by what I think is 3 more RFC's (red) spread over 2 MCB's, you need to switch off both to isolate these circuits so they're obviously cross connected, I think these were shoved in there to make way for the additions.
Then there's a selection of lighting circuits & an immersion.
Ideally I'd like to put in a new 16way CU but space is really tight due to the gas & water services in the vicinity so what can I do to sort this mess out? I will be replacing the trashy CU but can I double up any circuits and still give them full protection?
 

Attachments

  • Image0092.jpg
    Image0092.jpg
    104.7 KB · Views: 46
What a mess!

Just remember that a 'circuit' is what you make it, as long as the usual requirements are met regarding design current, protective device size, volt drop, current carrying capacity and earth loop impedance.

Are there really 5 rings in a domestic property?

At any rate, I'd want to do a full periodic before suggesting any remedials, god knows what else you'll find if the consumer unit is in that state!
 
Last edited:
What a mess that is.

If it is tight for space MK do a stacked cu basically two 8 way rails one on top of the other.


Sent from my iPhone using Tapatalk.
 
Good point about the 'circuit', I'll probably be able to combine a couple of the lesser lighting circuits easily enough.
It used to be 2 large apartments now it's only 1, that's probably why there's so many rings.
I'm going to test & assess everything beforehand and they're more than happy to address any problems found.

I don't think I can fit a stack in as the available depth is only 250mm, width is 330mm.
Is it acceptable to split the tails and take a few circuits to a slightly different location in a 4 way box for instance?
I was a bit shocked by the 2.5mm ring in the 40a with the 6mm and told them so, I have got my figures right on that haven't I?
 
Good point about the 'circuit', I'll probably be able to combine a couple of the lesser lighting circuits easily enough.
It used to be 2 large apartments now it's only 1, that's probably why there's so many rings.
I'm going to test & assess everything beforehand and they're more than happy to address any problems found.

I don't think I can fit a stack in as the available depth is only 250mm, width is 330mm.
Is it acceptable to split the tails and take a few circuits to a slightly different location in a 4 way box for instance?
I was a bit shocked by the 2.5mm ring in the 40a with the 6mm and told them so, I have got my figures right on that haven't I?

Yes, your sums are correct, 32A is the maximum for an 'A1 ring final'.

Splitting the tails to another consumer unit will allow you to comply with the 'division of circuits' regulation rather than doubling up lighting circuits.

Not the best situation but perfectly acceptable.
 
Cheers, I think I need to stare & poke at it for a while when I go back until I get that eureka moment :)
 
Apart from the cost issue would RCBo's offer more space? one of the companies do a slimmer RCBO, although I forget which one. You would have the added bonus of quickly identifying a fault on the correct circuit if there are any problems further down the line. I use RCBO's for every new CU change as I have had a couple brand new RCD's become faulty.
 
I bet that was done by the bellend who hardly spoke English when he asked me in screwfix car park "What do i need to wire up bathroom, I from Poland". I dont know whether or not he ever found a F*** O** but that is what i told him he needed.

Cheers...Howard
 
looking at that CU, just wondered if i still got paul daniels phone number.
 
personally i would stand back take a deep breath.. SIGH for a minute or two then isolate and say THIS IS GOING TO COST YOU!!!
 
I spent a couple of hours poking at it this morning & have decided to take the 6 new circuits (brown/blue) out & in to a new CU.
It's a right ******* state, you have to isolate 3 32a mcbs (I thought it was 2 at first) to cut the power to some ways & there's a 1.5mm lighting circuit in with the boiler on a 16a.
There's also a 16mm bond to a gas pipe on the left that hasn't been terminated at the met as it's too big to fit.
I found out that this was done by the same guy who installed some 5a/1.5mm socket outlets at another customers place and these were just spurred off the existing 32a/2.5mm rfc, ****.
 