neil123

do all spotlights need top hats on them if there is insulation in the roof space also does the transformer need a top hat as well
 
by top hats do you mean fire hoods? i would personally focus more on the correct ip ratied lights for the zone on the bathroom side and just clear the insulation from above the light in the loft
 
If you are changing the lights i would point out the benifits of haler LED IP68 rating 7 watts no lamps to change fire rated good all rounder
 
do all spotlights need top hats on them if there is insulation in the roof space also does the transformer need a top hat as well


Is this bathroom on ground floor?

If bathroom has a bedroom above it then use fire-rated spots, else not essential.

Must be correctly IP rated, and leave 75mm around the fitting free of Insulation.
 
There are several fire-rated fittings which are rated to have insulation over them now. If in doubt, use these.
 
you can't go by what a customer says. if they are within zones, they need to be IP rated. as far as insulation goes, bugger it off away from the lights.
 