Mrs wants a new socket directly below a light switch on the ground floor (says it will look neater vertically inline) spurred off the
downstairs ring, which all go up into that above ceiling/below floor space.
I gather I'm OK to do this as a (very experienced) DIYer? Or are we totally no-can-do these days?

Cable would be coming down the wall from up above, as is the cable to a four switch plate on an earthed metal backbox.
The wall is very thickly plastered brick (Victorian terrace - very thick party wall), and the four switch cables are in two 20mm oval conduits, with enough space between them (I think) that I could get a third 20mm conduit in between.
I've seen on another forum topic here that some might run that new spur cable down through the backbox - but some debate as to whether that was good practice (even with grommets).
One guy says he'd just run such a cable tightly around the outside of backbox, but that's not technically then in the permitted zone, and I don't like that idea.

I can't find an example of it anywhere, but I wondered about lifting the switch backbox out, gently chasing behind it into the brick (between the two screw holes and running the new cable in a 20mm conduit down the middle at the same depth as the two exiting conduits, but diving deeper into the brick just behind the switch backbox, and then coming back out to the normal depth below it until the socket backbox.

Is this a legit way to do this, or am I better to go through the switchbox with grommets?

Cheers for any advice here.
 
Personally, I wouldn’t run a power cable through a light switch box. Different circuits are permitted, but just doesn’t seem right.

Come round the side… Permitted zones extend horizontally from a switch or socket as well as vertically.

You don’t actually need conduit to run a cable in, although you will need to check that the sockets are rcd protected.

You might find an easier route going down to floor, rather than up to ceiling. Old house… wooden floor? I wouldn’t be surprised if there was a huge cellar.
 
Much appreciated.
Concrete floor, so down is no good (hopefully no mineshaft underneath!)
Going around the side of the switch box (and maybe I'm being over-worrisome) will it not stray just outside the permitted zone at the corners where it bends?
Also, does it matter if it's tight to the box or better to come away a cm or two from the box?
It seems wrong to be physically touching it - that's why I was considering conduit.
 
It’s fine touching the box, as close as possible.

I don’t fancy the idea of taking more brick out behind the box… might lose the bit where the fixings are.

No one will be likely to stick nails in the wall so close to a light switch.


I’ll mention again about RCD protection. Any new work on circuits must have this.

An old house, the sockets might also be in conduit. Has the place ever been rewired?
I’m thinking for ease of getting a new cable to a socket for spurring off.
(You don’t want hidden joint boxes under floors if you can help it)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Spur socket below lightswitch
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
BusyMartin,
Last reply from
BusyMartin,
Replies
4
Views
1,668

Advert

Back
Top