Got a look at a job today in a traveling site, we are installing a supply to a static caravan! The supply is tncs to a metal clad d/b in an out house,all circuits have rcbo protection!! There is a 100a rcd fitted,fed from the main isolator switch then feeding the d/b!! My ? is obviously the ze was very poor and this was put in at some point to overcome that, however with all circuits now protected by rcbos is the rcd still required?? Tight for space to install 4x4 box for the s.w.a supplying the van post.And forgive me if I'm being thick but how does fitting and rcd solve the high ze??

An an earth rod will be installed for the caravan supply tho!!
 
because a TT system will have a Ze value too high to trip a fuse/breaker in the event of a fault, a RCD will perform this function with a Zs of up to 1667 ohms for a 30mA device.
 
what does the existing RCD protect? is it there to protect the feeder cable to the DB?
 
Hi all,
Got a look at a job today in a traveling site, we are installing a supply to a static caravan! The supply is tncs to a metal clad d/b in an out house,all circuits have rcbo protection!! There is a 100a rcd fitted,fed from the main isolator switch then feeding the d/b!! My ? is obviously the ze was very poor and this was put in at some point to overcome that, however with all circuits now protected by rcbos is the rcd still required?? Tight for space to install 4x4 box for the s.w.a supplying the van post.And forgive me if I'm being thick but how does fitting and rcd solve the high ze??

An an earth rod will be installed for the caravan supply tho!!
The caravan supply needs to be a 30 ma double pole RCD as you have converted the supply to a TT system.
 
The caravan supply needs to be a 30 ma double pole RCD as you have converted the supply to a TT system.
The supply hasn't been changed yet that's my ? The 100a rcd is splitting the tails from the isolator then to the 100a main switch on a consumer unit with all circuits on an rcbo.
 
The supply hasn't been changed yet that's my ? The 100a rcd is splitting the tails from the isolator then to the 100a main switch on a consumer unit with all circuits on an rcbo.
But you said you were changing it ?
 
Had another look today was late last night and head was fried!! I think you must have miss read my original post tho!! I've kept the out house on the tncs supply and the caravan on tt!!! I said the caravan was being put on tt not the out house!! Which had the 100a rcd feeding the rcbo fuse board!! Was a strange setup should have posted a pic thanks tho.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland

Thread Information

Title
Static caravan
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
c.boy,
Last reply from
c.boy,
Replies
9
Views
1,957

Advert

Back
Top