Jimmyb

Im I missing something ?

been checking 2 x ring finals yesterday and found the following results :-


R1 Rn R2 R1+R2

0.36 0.36 0.45 0.18 for length of est circuit r1&rn values seem about right

0.47 0.47 1.38 0.35 cant check length with this but most be loose cpc somewhere

I thought well ill check for loose connection on both and found nothing, well I checked all accessible one/what I could find

anyone else got thoughts on this please there is only loose damaged connection
 
Have not read all of the post but firstly id be looking for any noticable alterations and starting there. It will more than likely be a poor connection in a junction box under floor boards or connections made of behind a kitchen unit for example. Or try following a logical route using "long lead" method and notin any considerable rises in test values to pin point the location of the fault
 
try following a logical route using "long lead" method and noting any considerable rises in test values to pin point the location of the fault
Follow a logical route, hmm... this is not always the case; I was doing this and going from socket to socket and got the rise in resistance logically between two sockets on the same wall 2 m apart, could not find the fault, then eventually took up the floor and found the ring went from one socket off to the end of the house, round the kitchen, upstairs, into the loft, back to the kitchen opposite wall through three more sockets and eventually back down to the other socket!
Obvious really when you (fail to) think about it.
 
Follow a logical route, hmm... this is not always the case; I was doing this and going from socket to socket and got the rise in resistance logically between two sockets on the same wall 2 m apart, could not find the fault, then eventually took up the floor and found the ring went from one socket off to the end of the house, round the kitchen, upstairs, into the loft, back to the kitchen opposite wall through three more sockets and eventually back down to the other socket!
Obvious really when you (fail to) think about it.

Upon finding nothing you should of thought 'maybe thats not the cable route' and followed the "non-logical" route :)
 
Follow this lack of logic!
[ElectriciansForums.net] Strange loop values
 
Follow this lack of logic!
View attachment 29758


Someones had a right laugh throwing that ring in! And i fully agree with you anyway pal. Worst is fault finding when alterations have been made on a ring main and you end up with sockets going from one room to the next, back downstairs, upstairs etc etc.
The joys of our job i guess!
 

Reply to Strange loop values in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top