managed to put a direct short across incomming L/N, and lost power, tested back to service fuse which was ok but i was getting 240v across L/N but as soon as i put a load on it dropped to about 110v, initial thoughts were id lost a neutral so rang dno.
Rapid response came out checked fuse - ok went next door where there was a 3 phase head and he also suspected a cable fault.
Linesmen came next (expecting road to be dug up) however the property was bunny hopped from next doors 3 phase head through a 40a fuse.
the fuse hadnt blown but was showing a high resistance, once replaced it was fine.
me and the dno guys couldnt understand how the fuse was sort of working yet not.