Where the measure of automatic disconnection is employed, fault protection may be provided by
1. Protective earthing only
2. Protective equipotential bonding only
3. Protective earthing and protective equipotential bonding
4. Electrical separation
I think 4 is the only one with a chance of working, bonding and earthing wouldn't work without ADS, need some way to disconnect the supply.
Separation would work if it puts things far enough apart there's no chance of a fault eg electricity pylons, although i doubt it's common in domestic.
i'd say#1 is the answer. some would argue #3, but bonding is not required for fault protection. bonding is there to prevent electric shock when in contact with both an exposed conductive part and a bonded service ( under fault conditions).
This is one of the instances where BS7671 needs to be sorted out. Changing from EEBADS to ADS was a joke.
Both EEBADS and ADS are protective protective measures which according to BS7671 require both basic protection and fault protection.
Basic protection is provided by basic insulation of live parts, barriers, enclosures, obstacles or by placing out of reach.
Fault protection is provided by protective earthing, protective equipotential bonding and ADS.
So for the question if the protective measure ADS is being used, there should already be in place protective earthing and protective equipotential bonding. That’s answers 1, 2 and 3 out of the way.
Other measures for providing fault protection are:
(i) SELV
(ii) PELV
(iii) FELV
(iv) double or reinforced insulation and
(v) electrical separation.
411.1 is just a description of a particular protective measure, there’s no requirement to provide that particular protective measure.
Also, installations can and do have more than one protective measure.
I would have put 3 but after reading the response by spinlondon it makes a sense.
I hate these questions, I personally think this question should be worded differently maybe mention ADS in the question to make it more clear.
Where the measure of "Automatic
Disconnection of Supply" is employed............
Is as though they're trying to be clever would be better to ask what other methods could be included, but the way I read it is you have an RCD at the board and they are now asking how do you create fault protection for your circuit, which you have no idea about location of or what it's for
I would say it is a bad question and they got the answer wrong.
The way I read the question is that a measure of automatic disconnection, not the protective measure "Automatic Disconnection of Supply", is in place what is needed to provide fault protection for this circuit.
Based on BS7671 the protective measure "Automatic Disconnection of Supply" has three parts listed under fault protection: protective earthing, equipotential bonding and automatic disconnection.
You have one in place and you need the other two to complete the requirements for ADS.
Answer 3.
Reply to Struggled with this one in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Question is does this DB really need RCD protection as there are only internal lights and sockets supplying this large building that used to be a...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Hello All. I am taking my 2396 written exam in December this year, therefore i am knee deep in practice papers. In case anyone else is in the...