iv been asked to install a sub-main to supply a house. The supply is quite far away from the house (40mtr) the cable will be installed direct in ground (SWA)
im abit rusty on my cable calcs and could do with some help and advice. hear is where i am at the moment...


ok so after applying diversity Ib = 91.5A and In=100A
so from table 4d4a multi-core armored 70'c refrence method D you get 99A for 25mm cable.

then volts drop mv/a/m = 1.75

so...
1.75 x 91.5A x 40 mtr /1000 to convert to volts = 6.405v

now if it was a final circuit not for lighting this would be ok (as it doesnt exceed 11.5v 5%). but its for a distribution circuit so if i was to then have other circuits running of it the volts drop would increase how do i account for this??

Read more: http://www.electriciansforums.net/e...3-supply-calculations-help.html#ixzz22QGLTbuq
 
yeh i understand it would be a larger CSA but would i need to calculate the volts drop on the circuits that will be connected to the supply and add to the supply cable??
 
Basically, if you are going to be connecting lighting to this supply, then your VD allowance should take this into account (3%).
 
Last edited by a moderator:
  • Like
Reactions: 1 person
I would say so. If your lighting circuit is another 20m, then its at the end of this where your volt drop needs to be within limits.
 
ok so after applying diversity Ib = 91.5A and In=100A
so from table 4d4a multi-core armored 70'c refrence method D you get 99A for 25mm cable.

then volts drop mv/a/m = 1.75

so...
1.75 x 91.5A x 40 mtr /1000 to convert to volts = 6.405v



I would say you'll be lucky to see 91.5A being drawn from any standard domestic supply!! 99% of the time you would still be lucky to see 60A, and then only for a matter of a few minutes...

 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Sub-main calculation help!
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
energizedelec,
Last reply from
Engineer54,
Replies
5
Views
2,691

Advert