energizedelec

iv been asked to install a sub-main to supply a house. The supply is quite far away from the house (40mtr) the cable will be installed direct in ground (SWA)
im abit rusty on my cable calcs and could do with some help and advice. hear is where i am at the moment...


ok so after applying diversity Ib = 91.5A and In=100A
so from table 4d4a multi-core armored 70'c refrence method D you get 99A for 25mm cable.

then volts drop mv/a/m = 1.75

so...
1.75 x 91.5A x 40 mtr /1000 to convert to volts = 6.405v

now if it was a final circuit not for lighting this would be ok (as it doesnt exceed 11.5v 5%). but its for a distribution circuit so if i was to then have other circuits running of it the volts drop would increase how do i account for this??

Read more: http://www.electriciansforums.net/e...3-supply-calculations-help.html#ixzz22QGLTbuq
 
yeh i understand it would be a larger CSA but would i need to calculate the volts drop on the circuits that will be connected to the supply and add to the supply cable??
 
ok so after applying diversity Ib = 91.5A and In=100A
so from table 4d4a multi-core armored 70'c refrence method D you get 99A for 25mm cable.

then volts drop mv/a/m = 1.75

so...
1.75 x 91.5A x 40 mtr /1000 to convert to volts = 6.405v



I would say you'll be lucky to see 91.5A being drawn from any standard domestic supply!! 99% of the time you would still be lucky to see 60A, and then only for a matter of a few minutes...

 

Reply to Sub-main calculation help! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Domestic property Supply number 1 6 flood lights 4x400watt= 1600 watts 250meters from board to closets corner of tennis courts Tennis court...
Replies
18
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock