Never seen a three phase CU and the pump is not likely to need an RCD.
Mcbs are not likely to achieve selectivity. Using such devices for distribution is a poor design.Just a CU with a three phase RCD to supply the three phase air pump and to distribute the single phase's to the other CU's.
Each subsequent CU to have a single phase RCD or as many as you want.
Sounds like the client has already obtained the parts so other options are not likely to be favoured.
It's how I was instructed to do it by the French "Conusule" who are the regulating body in France, the incoming main is into a S type RCD at the meter this is EDF equipment you have no choice.
It's how I was instructed to do it by the French "Conusule" who are the regulating body in France, the incoming main is into a S type RCD at the meter this is EDF equipment you have no choice.
I had this argument with someone a while ago, he wanted to protect a sub main to a summer house with a 40A MCB in the consumer unit and I was saying that if the 6A lighting circuit has a problem it could well trip the 40A MCB before the 6A one, it just depends which is the quickest to go.Mcbs are not likely to achieve selectivity. Using such devices for distribution is a poor design.
Selectivity will be poor, but sometimes it comes down to how important it is. For an occasional summer house it is probably acceptable risk, but not for many circuits in a home where loss of stair lighting, etc, has other hazards.I had this argument with someone a while ago, he wanted to protect a sub main to a summer house with a 40A MCB
Once you get pas the slow thermal trip side, many MCCB have a short-delay aspect (sometimes adjustable) of 20ms or so at modest overload currents, then once you hit really big faults in the kA range they go on an "instant" trip in the 10ms or less region to energy-limit the fault, just as MCB do.Are MCCB's less "sensitive" than an MCB then like fuses are, I'm no expert in commercial stuff.