If you are looking at a low-ish power sub-main for a garage, etc, you have the trade off between:
- The easy option of taking the feed cable from a MCB in the CU
- The bigger cost/effort of splitting the tails and adding a fused switch to feed it
Both are safe, but achieving discrimination between two MCB is series is
much harder to do as the main one's instantaneous magnetic trip is quite likely to be reached before the downstream breaker has cleared the fault.
A few MCB suppliers publish tables to show the sort of fault current where they are able to discriminate to, but it is not that dependable. Also Schneider have an on-line tool to help compute for their MCB (as well as and BS88 fuses, etc) which I will try to link to but they have gibberish style addresses and it seems not to work with Firfox so you might have to seel your soul to Google and use Chrome web browser:
Electrical Calculation Tool - https://hto.power.schneider-electric.com/cbt/app/index.html?code=34a79e11-548d-4e49-8a1e-10f9fa18492b&client_id=cbt#/Dashboard
To get any hope of a selective response for MCB in cascade try to keep the upstream one as high as the feed cable is safe for and go for a 'D' curve if you can at all meet the disconnection times (for a sub-main I guess that is 5s), and then try to keep the local breakers as small as you sensibly can (say 20A 'B' curve for any ring in the garage).