- Reaction score
- 6,445
Have an existing old client with what's best described as a sprawling small-holding of a property.
There's an armoured external supply which branches into a submain for various sheds/workshops/stables (some of which are 150-200m) etc all of which have standard RCD final circuit protection and all the feeders are SWA, so there's not really a design need for an upfront RCD coming out of the house, except.... naturally the outgoing SWA only starts on the opposite side of the building to the CU, when the original builder put it all in there's standard 6242Y going from the CU through the fabric of the building to feed it - so that does require 30ma protection. Needless to say, this is leading to nuisance tripping of the feed RCBO in the CU.
Board is an all RCBO Easy9 that I updated to a couple of years ago, and Schneider naturally don't make anything so sensible as an S type RCBO for them (have asked technical). If I fit an external unit to the CU it will have to be a mess of replace RCBO for MCB > OUT > RCBO > Back in again and joint to the 6242Y. Equally, running a new length of SWA out and jointing on to the external feeder isn't really an option either as it would involve significant ground works.
Suggestions welcome! R.