But that is not what you posted. To me as you quoted the 1667 ohms thing which is what is measured between exposed conductive parts and extraneous conductive parts you were asking about that.

You then seem to be complaining that people are not answering a completely different question about what makes a conductive part extraneous.

Which question are you asking?


First time on this forum so apologies if I'm not being clear.

My question is who actually carrys out the testing to see if supplementary bonding to extraneous conductive parts in a bathroom is required when there is full RCD protection
 
But that is not what you posted. To me as you quoted the 1667 ohms thing which is what is measured between exposed conductive parts and extraneous conductive parts you were asking about that.

You then seem to be complaining that people are not answering a completely different question about what makes a conductive part extraneous.

Which question are you asking?


First time on this forum so apologies if I'm not being clear.

My question is who actually carrys out the testing to see if supplementary bonding to extraneous conductive parts in a bathroom is required when there is full RCD protection
 
First time on this forum so apologies if I'm not being clear.

My question is who actually carrys out the testing to see if supplementary bonding to extraneous conductive parts in a bathroom is required when there is full RCD protection

Supplymentary bonding is not required for extraneous conductive parts (unless they are within touching distance of exposed conductive parts and the resistance between the two is greater than 1667 ohms) Main equipotential bonding is.
 
your question is technically incorrect that’s why you aren’t getting many answers. Your opening post says exposed when really it should say extraneous. You’ve specifically mentioned bathrooms when you should be checking for extraneous conductive parts throughout the whole installation. To answer your question...I bond all extraneous conductive parts back to the MET with an appropriately sized conductor, 30mA RCD protection is provided and my circuits are under max EFLI values then I know my installation is correct. If these 3 points are met then I do not need to worry about supplementary equipotential bonding in the bathroom. You seem to be confused about the actual requirements.... A simplified version of your opening post, would of said “ do you test for extraneous conductive parts that require bonding?”

Exposed pipe work that requires supplementary bonding in a bathroom to me would
Supplymentary bonding is not required for extraneous conductive parts (unless they are within touching distance of exposed conductive parts and the resistance between the two is greater than 1667 ohms) Main equipotential bonding is.


Do you carry out the tests
Supplymentary bonding is not required for extraneous conductive parts (unless they are within touching distance of exposed conductive parts and the resistance between the two is greater than 1667 ohms) Main equipotential bonding is.

My point exactly but how many electricians actually know that? As i believe allot think that having rcd protection alone ommits the need for supplementary bonding.?
 
Many electricians will have automatically ensured that main protective bonding is in place as this is required for all ADS protected circuits, not just bathrooms, and the same applies for all the circuits in the installation that they meet the disconnection times.
These should be in place before you start considering bathrooms, it is at this point that any testing for extraneous conductive parts would have been undertaken.
Then when considering bathrooms 30mA RCD protection is required; ensuring this is also included would then mean that supplementary bonding in the bathroom could be omitted.
Testing for extraneous conductive parts again in the bathroom would not be necessary because it has already been done.
This is not to say that some electricians would assume all main protective bonding is in place and that ADS times are met and so state that 30mA RCD protection is all that is required.

So to answer the question you intended to pose, the testing for extraneous conductive parts would be done earlier and not necessarily in the bathroom as it is the point of entry into the installation of the extraneous conductive part that is the point requiring bonding.
The testing would still be completed, just not in the manner you propose.
 