Ian1981
And the IET agree that they don’t need earthing , if you read GN8 tray, basket and the like containing / supporting cables which are insulated and sheathed and fulfill the requirements of double insulation do not require earthing.
You certainly wouldn’t provide protective bonding to them as they are unlikely to be extraneous conductive parts either.
The bottom line is that in most cases they do not form part of the electrical installation
You certainly wouldn’t provide protective bonding to them as they are unlikely to be extraneous conductive parts either.