I wasn't taught about 'path of least resistance', I was taught the science of electricity, ohms law etc.
Electricity does not 'take the path of least resistance' it splits between all available paths and the current in each path is proportional to the resistance.
It is actually directly proportional to the admittance. Or inversely proportional to the resistance if the reactance is negligible.
 
@OP Chris Kitcher has some good stuff on determining if a metallic part is extraneous.

I wasn't taught about 'path of least resistance', I was taught the science of electricity, ohms law etc.
Electricity does not 'take the path of least resistance' it splits between all available paths and the current in each path is proportional to the resistance.
Yes unfortunately touch voltage isn't really taught try reading some electrical engineering books I can provide some links if you want.
[automerge]1596147018[/automerge]
and this is wrong if you were wet standing bare foot on the ground in direct contact with mass of earth you would be getting a nasty/fatal shock you would be the path of least resistance to earth.
 
Last edited:
@OP Chris Kitcher has some good stuff on determining if a metallic part is extraneous.


Yes unfortunately touch voltage isn't really taught try reading some electrical engineering books I can provide some links if you want.
[automerge]1596147018[/automerge]
and this is wrong if you were wet standing bare foot on the ground in direct contact with mass of earth you would be getting a nasty/fatal shock you would be the path of least resistance to earth.

You are missing my point entirely.

My point is that "electricity follows the path of least resistance" is a nonsense, electricity follows all available paths. The division of current between available paths is defined by specific laws of science.

Yes, we can all come up with abstract scenarios where a fatal shock is guarateed regardless of protective measures put in place.

Yes of course If you stand naked in the rain on ground with a bonded metal pipe buried 25mm below the surface of the conductive clay you are standing on whilst poking a wire coat hanger into the L1 socket of a 125A TPN socket you will probably die.
 
My point is that "electricity follows the path of least resistance" is a nonsense, electricity follows all available paths.
Yes of course If you stand naked in the rain on ground with a bonded metal pipe buried 25mm below the surface of the conductive clay you are standing on whilst poking a wire coat hanger into the L1 socket of a 125A TPN socket you will probably die.
....... whilst peeing in a puddle? ;)
 
After Dave's post you know he's quite a argumentative chap :p I did a little googling and it seems saying current takes the path of least resistance does get some peoples backs up and it's perhaps better to say More current will flow in the path of least resistance or even better more current will flow in the path of least impedance, I think it's a bit picky because I don't think anyone is assuming all current will flow down one path but the majority.
[automerge]1596150415[/automerge]
however saying Current takes the path of least resistance when talking about earthing something metal might seem like saying all the current will take that path, I concede to that.
 
Last edited:

Reply to Supplementary bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
371
Just a thought guys in terms of RCBO’s and supplementary bonding. Obviously supplementary bonding isn’t required as long as a 17th / 18th...
Replies
5
Views
2K
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock