Just a thought guys in terms of RCBO’s and supplementary bonding.

Obviously supplementary bonding isn’t required as long as a 17th / 18th condition consumer unit is fitted (dual RCD protecting all circuits) but what if it’s a main switch only with individual RCBO’s?

What is stopping somebody from installing an MCB leaving users at risk under fault conditions?

As they’re forced to install an MCB on a dual RCD board the user is covered but what if they haven’t got an RCBO on the back of their motor instead installing an MCB on a main switch only consumer unit?
 
Nothing to stop a mcb being installed but the installer should be aware that additional protection will be compromised,as would no (RCD) Residual Current Device to domestic lighting . If no exposed and extraneous conductive parts are simultaneously accessible I don’t see it’s a problem.
 
Just a thought guys in terms of RCBO’s and supplementary bonding.

Obviously supplementary bonding isn’t required as long as a 17th / 18th condition consumer unit is fitted (dual RCD protecting all circuits) but what if it’s a main switch only with individual RCBO’s?

What is stopping somebody from installing an MCB leaving users at risk under fault conditions?

As they’re forced to install an MCB on a dual RCD board the user is covered but what if they haven’t got an RCBO on the back of their motor instead installing an MCB on a main switch only consumer unit?

Nothing you can do about it. If someone is going to fit an MCB because they don't happen to have an RCBO then there's no hope!

You might as well say you won't fit an FCU because someone might change the 3A fuse for a 13A one
 
Obviously supplementary bonding isn’t required as long as a 17th / 18th condition consumer unit is fitted (dual RCD protecting all circuits) but what if it’s a main switch only with individual RCBO’s?
I'm all for short and simple explanations of regs but that is simplifying things a little bit too far!
That is only 1 of 3 requirements in order to omit supplementary bonding in a room containing a bath or shower. I'm sure you know this already but trainees read this forum too.

What is stopping somebody from installing an MCB leaving users at risk under fault conditions?
Bottom line is that good electricians take the time to understand the whole installation including the supply before modifying a part of it. There will always be some that won't. We can only live in hope that an EICR by someone more knowledgeable takes place before any harm comes of it.

I've previously found a RCBO board on a TT system where the heat source pump people chucked an MCB in it, thus meaning their sub-main, CU and the gear they installed had no fault protection.

but what if they haven’t got an RCBO on the back of their motor instead installing an MCB on a main switch only consumer unit?
No one is forced to fit the wrong device in a consumer unit. I have no shame in saying that I haven't got the right part and I'll have to return. It's a right pain sometimes, especially if you try and plan ahead and take what you need and it doesn't work out, but it's a reality of our job!
You might as well say you won't fit an FCU because someone might change the 3A fuse for a 13A one
I've unwittingly done the opposite once - I was half way home when I remembered the 3A fuses were still in my pocket after buying them at lunchtime and realising I'd not put one of them in the FCU for the extractor.....!
 
I've previously found a RCBO board on a TT system where the heat source pump people chucked an MCB in it, thus meaning their sub-main, CU and the gear they installed had no fault protection.
I would think it would help in the event of a L to N fault though :)
 

Reply to RCBO’s and Supplementary bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
369
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock