(ii) one socket-outlet or connector complying with BS EN 60309-2 which is interlocked and classified to
clause 6.1.5 of BS EN 60309-1 to prevent the socket contacts being live when accessible,
??
 
Bs 7871 allows an interlocked socket.


722.55.101.0.201.1 Each AC charging point shall incorporate:
(i) one socket-outlet complying with BS 1363-2 marked ‘EV’ on its rear and, except where there is no possibility
of confusion, a label shall be provided on the front face or adjacent to the socket-outlet or its enclosure
stating: ‘suitable for electric vehicle charging’, or

(ii) one socket-outlet or connector complying with BS EN 60309-2 which is interlocked and classified to
clause 6.1.5 of BS EN 60309-1 to prevent the socket contacts being live when accessible, or
(iii) one socket-outlet or connector complying with BS EN 60309-2 which is part of an interlocked self-contained
product complying with BS EN 60309-4 and classified to clauses 6.1.101 and 6.1.102 to prevent the socket
contacts being live when accessible,
 
Yes but the Code of Practice only permits them in non-domestic installations.
 
Yes but the Code of Practice only permits them in non-domestic installations.

The intent of 553.1.201 is to prevent things from being poked into the outlet.

If the outlet is interlocked, then its compliant.
 
Compliant with what?
 
With bs7671. as @ #22

The OP asked if his proposal was compliant, no it is not. Sockets outlets for households shall be shuttered according to BS7671 unless you can show me a clause for 553.1.201 which says different.
EN 60309-2 socket outlets can be used for EV chargers in non-domestic installations according to the Code of Practice.
Now if you want to install one of these sockets in a dwelling I don't really care that is your perogative but for the purpose of this thread and which has been repeated on other threads it would not be compliant. No doubt you will still want to get the last word in.
 
Status
Not open for further replies.

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Status
Not open for further replies.
Title
Fully reversible install
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26

Thread Tags

Tags Tags
install

Advert

Thread statistics

Created
evstruggler,
Last reply from
westward10,
Replies
26
Views
623

Advert