TJ Anderson thanks for response. My response you highlighted doesn't read well. I will try to explain better for discussion. That's what it is discussion not criticism.
When meter tails are over 3m an isolator is normally needed to satisfy the dno.
If the tails were split with say swa cable and a neat way was found to terminate the swa without the need of a fused switch then what is the difference between the new swa tails and the existing house tails? If they the same rating?
The difference the swa is actually better protected than the original tails that run for 15 meters through the house.
The discussion was if the new tails absolutely have to have a fused switch then why is just an isolator acceptable for every other property in the uk with meter tails over 3m.
I will be using a fused switch, I will be changing cable size to xlpe because of its increased rating I will be TTing the system.
The reason for the TT is its safer.

I can speck the install 100 percent because he doesnt know how many chargers he wants in the future. Most probably 2 but not ruled out more.
I hold my hands up to not knowing the true capabilities of xlpe cable over standard swa but I have now been educated

Discussion forum not criticism forum. People come on for help and advice in improving installs not to be picked apart otherwise what's the point.

Thank you. I apologise for my outrageous behaviour.

Absolutely......Let's continue our discussion.....

I am pleased to hear about your revelation regarding XLPE SWA. Amazing stuff it is. Can you educate me as to the equipment you are now designing to run at 90 Degrees Celsius? I have never got to do that in my limited electrical dabblings as I struggled to find suitable reasonably priced items for garages and garden shed installs etc

Why is TT safer here, we only have that PME at work. Am I in danger, I really don't understand??
[automerge]1595116417[/automerge]
Thankyou now that is what I call a well constructured reply. Explains the point very clearly and explains my question.

Again, I'm terribly sorry and I'd like to add the irony of this was not lost on me.
 
Thank you. I apologise for my outrageous behaviour.

Absolutely......Let's continue our discussion.....

I am pleased to hear to hear about your revelation regarding XLPE SWA. Can you educate me as to the equipment you are now designing to run at 90 Degrees Celsius? I have never got to do that in my limited electrical dabblings as I struggled to find suitable reasonably priced items for garages and garden shed installs etc

Why is TT safer here, we only have that PME earth thing at work. Am I in danger, I really don't understand??
A
Thank you. I apologise for my outrageous behaviour.

Absolutely......Let's continue our discussion.....

I am pleased to hear about your revelation regarding XLPE SWA. Amazing stuff it is. Can you educate me as to the equipment you are now designing to run at 90 Degrees Celsius? I have never got to do that in my limited electrical dabblings as I struggled to find suitable reasonably priced items for garages and garden shed installs etc

Why is TT safer here, we only have that PME at work. Am I in danger, I really don't understand??
Really helpful king of person. Thanks.
Two quotes. You don't know what you don't know.
And don't judge someone on their worst day to you on your best.

Now rather than criticising either help my understanding or go away. You hold the 2396 so you are perfectly capable of explaining.

I would try and explain my reasoning but sure you would just RIP it apart with no explanation.

I don't know your background and will not guess but I often find the best designers are the worst installers and the best installers are the worse designers.

Goodnight.
 
For fear of this turning into a keyboard fight and getting moderated i would suggest to the OP (and am sorry if this upsets you as it is meant as positive criticism), but having read 2 pages of posts I do believe the job is beyond you; certainly from a design perspective at any rate.

Your original post details a very standard type of installation that we as sparkies often do, but your questions and comments do indicate it is something you have possibly not yet tackled before. Can you not get a more experienced contractor to let you shadow them and see how it’s done? Maybe someone from the forum can help?
 
For fear of this turning into a keyboard fight and getting moderated i would suggest to the OP (and am sorry if this upsets you as it is meant as positive criticism), but having read 2 pages of posts I do believe the job is beyond you; certainly from a design perspective at any rate.

Your original post details a very standard type of installation that we as sparkies often do, but your questions and comments do indicate it is something you have possibly not yet tackled before. Can you not get a more experienced contractor to let you shadow them and see how it’s done? Maybe someone from the forum can help?
Was having bad day yesterday. Little.one went to hospital with peanut reaction so will take it o the chin.
Mr TJAnderson has opened my eyes to looking at it from a different perspective and he is entirely correct in his xlpe comment on cable selection.
I have got another very experienced contractor to aid in this but wanted to explore all options in open environment.
I think the forum would a better place if instead of people just saying why or wouldn't do that they explain their own view and reasoning as in with pme. Which has been discussed numerous times on many forums and always results in differing opinions.
Any more information on exporting pme that is concrete and not a personal view would be appreciated.
 
Also it is not a "standard circuit" that you can just look in the OSG table for a yes/no based on load, length and CSA.

There is the special location side - the whole CPC from PME in another location with or without extraneous conductive parts bonding to worry about.

Then you have the simple circuit, say a couple of sockets and FCU for lights fed from house CU slot, versus a sub-main to a 2nd CU/DB and the whole OCPD/RCD selectivity arguments that go with planning that.
 
@Edward67 hope the little dude is ok, really worrying when as a dad you can’t fix it and have to trust others.

The forum works best (imho) when someone says whom they are, their experience and then ask for help, having shown their calculations and described what they are to achieve or drawn a diagram etc. Part of the problem is that there are too many DIYers on here pretending to know something when they clearly don’t (I’m in no way suggesting that’s you).

I hope you keep posting questions ?
 
@Edward67 hope the little dude is ok, really worrying when as a dad you can’t fix it and have to trust others.

The forum works best (imho) when someone says whom they are, their experience and then ask for help, having shown their calculations and described what they are to achieve or drawn a diagram etc. Part of the problem is that there are too many DIYers on here pretending to know something when they clearly don’t (I’m in no way suggesting that’s you).

I hope you keep posting questions ?
Ok will attempt to post with more depth in future.
 

Reply to Supply to garage. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
908
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
888
A friend of mine wired a 10mm 3 core armoured cable to his shed before I got involved and wired it himself already. He wants make it an air bnb...
Replies
8
Views
922

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock