Hi Fellas

Sure i had another login but seems my account has been recycled......anyway.

Im running a supply to multiple portacabins and shipping containers.

The Supply is a TNS and is approximately 95m away.
I have decided on a 63A 3phase circuit and calculated the cable size @ that length to be 25mm (total volt drop at this distance is 11.5v (Calculated)).

It will be supplying a new DB which will be enclosed in an Ip rated enclosure and separate circuits to be supplied to each of the units/containers.

Ok so now my question, i have been reading the regs and guidance notes regarding this and it clearly says no PME which i completely understand, But what about a TNS supply?

I get that there can be a difference in potential between the earth supplied and the true earth but if theres an Earth rod for each unit.

I personally cannot see why this is not acceptable but please let me know what you guys think in this situation.

cheers

Darren
 
You might want to recheck with regards to volt drop as well. 11.5 just on the distribution circuit means all the circuits off the connect DBs will be below the required minimum especially the lighting.
 
TN-S is fine. the reason PME is frowned on is that a loss of the supply N ( and hence the site earth) would lead to the metal structures possibly becoming "live".
 
Using 50mm 70c SWA will bring you volt drop down to 5.56, this gives you something to play with. This isn't taking into account of VD from source of supply to your DB.

That was using R for a resistive load.

Do you know what loads will be applied to the circuits as this will have a large impact on your VD calculations. You could get cheeky with the diversity to get the CSA down a little.
 
Literally a few ringmains, heaters and lighting ccts.

Using Z or R are the same 2.5 Mv/63A/90M thats worse case....

50mm cable is a big jump and @90m is 7.75 VD which is already more than 3%

If i drop the current down to 40A its still 6.4VD

Seems ridiculour that it would end up being 70mm+ for a few circuits?
 
It is a pain to work out, also adding correction factors for burial etc. Just as you get it sussed you finish off with the adiabatic and that sends you back to square one!!!

Oh, and ignore my calc, I was looking at the wrong column which doesn't help!!!
 
lol i did wonder....

lets assume the VD was all good the answer to my original question is yes to TNS yes? and do i need to add earth rods or not? i feel like i should
 
IMG_20170925_194949.jpg


I like the wording of this paragraph.....(the bottom one)

I dont envisiage any of the load per phase to exceed 20A and therefore the results are going to differ tot he tabulated values.

what you think? i know i'm clutching.....

Dropbox - IMG_20170925_194949.jpg - https://www.dropbox.com/s/46ym3q6xiiauyob/IMG_20170925_194949.jpg?dl=0
 

Reply to Supply to Portable buildings and portacabin/container in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
1K
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
677
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock