hi all,

end of last year as part of some agri work we had to re supply some barns. changing nothing to their install individually but from an overhead to underground SWA.
Another spark has been there to work on some new install in some offices. he has said to the tenant farmer that we should have installed surge protection at each of the points we have re fed, halfway along a 160m run is a barn that has a socket and light then it terminates to a workshop that has a typical framers approach TT systems obviously and divorced earth as origin is PME. As the farmer is not paying it for these works instructions are as normal to keep costs to a minimum.
Im questioning myself but I don't see why we should have if just re feeding an existing system?
any advice appreciated.
 
hi all,

end of last year as part of some agri work we had to re supply some barns. changing nothing to their install individually but from an overhead to underground SWA.
Another spark has been there to work on some new install in some offices. he has said to the tenant farmer that we should have installed surge protection at each of the points we have re fed, halfway along a 160m run is a barn that has a socket and light then it terminates to a workshop that has a typical framers approach TT systems obviously and divorced earth as origin is PME. As the farmer is not paying it for these works instructions are as normal to keep costs to a minimum.
Im questioning myself but I don't see why we should have if just re feeding an existing system?
any advice appreciated.
I suggest you read the IET guidance mote 1 OSG 3.7.2.1 Regulation 443. 1,443.2 and 443.4 which states where SPDs "may not be needed"
Followed by OSG 3.7.2.2 "Where SPD protection is required"
The flow chart on 3.7.2.2 OSG should help with your question,
 
Generally SPD is a good thing, but depending on the region (for lighting activity level), feed arrangement (for susceptibility to picking it up), and connected equipment (risk of damage and impact of any), you may not be able to justify it.

As Pete999 has pointed out, the IET 18th has a flow chart and other info for guidance.

If there is no history of trouble you could reasonably assume it is not needed, more so going from overhear to SWA where the risk of pick-up is lower.
 
Generally SPD is a good thing, but depending on the region (for lighting activity level), feed arrangement (for susceptibility to picking it up), and connected equipment (risk of damage and impact of any), you may not be able to justify it.

As Pete999 has pointed out, the IET 18th has a flow chart and other info for guidance.

If there is no history of trouble you could reasonably assume it is not needed, more so going from overhear to SWA where the risk of pick-up is lower.
Indeed having read through prior we came to decision it wasnt needed. Very low risk of lighting, literally very little vulnerable equipment (handful of led floods) No livestock being arable farm.
[automerge]1595411360[/automerge]

[automerge]1595411466[/automerge]
Also, the supply the farm is now under ground, so no over head
 
Anyone got the flowchart at hand, or is it online? My 18th is back in the house.
Ive got heaters to go into a village hall.... some existing circuits, some new.. 3ph board but all single phase circuits.
The additional circuits will fill the board to capacity....

I dont think it needs an SPD, just general lighting and power, kitchen, all electric heating.
The groups that use the hall will bring their own equipment, but usually nothing more than a CD player for the pilates group.
 
Anyone got the flowchart at hand, or is it online? My 18th is back in the house.
Ive got heaters to go into a village hall.... some existing circuits, some new.. 3ph board but all single phase circuits.
The additional circuits will fill the board to capacity....

I dont think it needs an SPD, just general lighting and power, kitchen, all electric heating.
The groups that use the hall will bring their own equipment, but usually nothing more than a CD player for the pilates group.
OSG has one I carry mine with me, or used to when I was active
 
Anyone got the flowchart at hand, or is it online? My 18th is back in the house.
Ive got heaters to go into a village hall.... some existing circuits, some new.. 3ph board but all single phase circuits.
The additional circuits will fill the board to capacity....

I dont think it needs an SPD, just general lighting and power, kitchen, all electric heating.
The groups that use the hall will bring their own equipment, but usually nothing more than a CD player for the pilates group.
If it’s a new installation Then you need to do a risk assessment, if you don’t , then the installation shall be protected against transient overvoltages etc etc.
For a few new circuits added then it’s not necessarily required.
 

Reply to surge install or not (farm) in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Our farm has a main 200 amp panel in the barn which services the barn, an addition to the barn with an apartment, an herb-gardening facility, and...
Replies
12
Views
1K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back...
Replies
7
Views
863
This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...
Replies
9
Views
2K
We have had RG11 installed in some flats for use with Virgin/Internet. It should I think have been RG6 but the guy at Virgin was insistent it...
Replies
4
Views
366

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock