Someones installed a swa for a lift/ramp in a garage but not used any banjos either end.

its a 5 core cable (brown black gray g+y blue) it's glanded to a metal db on end, and a plastic isolator the other, now should it have banjos and fly leads both ends or just the plastic end or not at all as the sheath is connected via the gland at the metal db? Also as its 3-phase should it be phased marked as in brown marking on each live wire? Or just left brown black gray?

bit of a gray area in my head...

Any help? Cheers
 
Wot I like doing if I have a metallic db is i allways if possible have peace of trunking above dis board gland and banjo all swa's to the trunking ( no earth tail to each banjo in the instance below if I were to gland swa's to a db solely probably would earth tail each ) and usually earth the trunking via the banjo of the supply swa . I always remove paint as tidy as possible at db side when glanded directly .

ImageUploadedByTapatalk1378153046.739247.jpg

I trust the trunking to to supply a reliable sound interconnection of earth between glands but yes have a earth tail to trunking usaly same csa as MEC .

This last pic is a mystery had uploaded it as a mistake and deleted it but its still there ????? No relevance
 

Attachments

  • ImageUploadedByTapatalk1378152857.957950.jpg
    ImageUploadedByTapatalk1378152857.957950.jpg
    200.7 KB · Views: 112
Last edited:
"But having said that I will agree that after reading that i would need to start fitting banjo's or earth nuts in the future".

Yup.

At both ends mate with a 6mm brass nut and bolt either tapped or drilled through the banjo and box(paint removed with file and contact grease applied of course lol).

You then take a fly lead from the 6mm bolt and armouring to the internal earthing terminal of the board...........sized accordingly.
You then have your internal earth as your cpc and your swa as a cpc(if required) and they can then both be a bond and vice versa.............complimenting each other as it were:)
Then you have the parallel paths and disconnection times in a nano second.......................................................

Or you can just use the Swa as your cpc of course:)
 
had to replace an isolator in a wash up area of a hot it had a TPN switch right next to a dishwasher water every where the armour was the CPC , I replaced the isolator with a rotary IP rated switch used the earthing nut tightened the grub crew earth tail to earth block and tadarr job done spot on continuity readings and Zs happy days
 
Un earthed SWA armouring to the main earthing terminal in the plastic DB is a non conformance on the inspection assessment for the inspection and test course, if you dont pick it up you will fail, so read into that what you will.

Cheers..........Howard
 
if non-metallic boxes, tag at one end if you just want to earth it. tag both ends if it's being used as cpc.
 
had to replace an isolator in a wash up area of a hot it had a TPN switch right next to a dishwasher water every where the armour was the CPC , I replaced the isolator with a rotary IP rated switch used the earthing nut tightened the grub crew earth tail to earth block and tadarr job done spot on continuity readings and Zs happy days

So what your saying is the IP rating wasn't correct from the initial install but it is now:)
Shrouds and outside IP rated glands to IP56(ships deck) if there was water everywhere? :):thinking2:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
SWA cables and banjos!
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
45
Unsolved
--

Advert

Thread statistics

Created
ewatty,
Last reply from
Engineer54,
Replies
45
Views
13,531

Advert

Back
Top