Definitely DNO if your thinking of taking 100A from an existing head! If its single phase that is
 
Cant believe no-ones asked what the Ib is , which is the starting point for any cable selection.

without it , the job is going no-where TBH.
 
Probably because it would only be a guess!! after diversity i comes out at something like 150A which is why the maths dont work!!
 
Its one of the thing i never understand when you add all the loads up on any home take away the diversity percentages you are still over the head rating!!
 
Thanks all for your help/advice i will speak with the owner if he still requires such high demand the DNO it is!
 
.4 being 120mm2 drop of 8.4V? hefty cable!

- - - Updated - - -

good job it wont be my money!!
 
OK, so tell what loads are expected, and we can go from there.
i can't imagined a stable block requiring a huge demand
.

i can.

build some stables on a greenfield site and you then have an established footprint of an existing building. then, a few years down the line, apply for change of use and get planning permission for a house. and, oh look, we've already got a 100A supply, how convenient!
 
when you do get your definite max demand figures, don't forget that it could still be cheaper to run it with parallel supplies, ie 4 core SWA. Also the larger size doesn't need to go all the way from source to load. You can take minimum cable size for fuse a short distance, connect it to upsized cable for the long run, then downsize it back for final connection to load. 140m is a long way; hope it's being trenched, and not ducted!!
 