bristolsparky
hi guys hope one of you chaps can help.....
I am on a job where we are currently doing 1st fix to five new build flats in stud walls throughout,
The developer and architect have cocked up somewhere and on the plans i have it clearly states that there os 600mm duct for all the submains to main busbar chamber but the ducting very clearly has not been installed. So now we have to pull in the submains through the stud work/joists etc....
I dont see why i need armour cable as now it is not buried and as concealed in the stud walls/floor and will be rccb protected the longest run by the way no more than about 20 metres and all are very small flats no more than 60amps. Please can you lot give more your advice on this as swa it triple the price and job is very tight!
Also what would be the best bonding arrangement i guess a big MET wall mounted and connect to main cpc then from MET to gas and water meters and then to the submains db and then from the submains db off to seperate cpc to their own db or the gas and water bonded twice from flats db?
I am on a job where we are currently doing 1st fix to five new build flats in stud walls throughout,
The developer and architect have cocked up somewhere and on the plans i have it clearly states that there os 600mm duct for all the submains to main busbar chamber but the ducting very clearly has not been installed. So now we have to pull in the submains through the stud work/joists etc....
I dont see why i need armour cable as now it is not buried and as concealed in the stud walls/floor and will be rccb protected the longest run by the way no more than about 20 metres and all are very small flats no more than 60amps. Please can you lot give more your advice on this as swa it triple the price and job is very tight!
Also what would be the best bonding arrangement i guess a big MET wall mounted and connect to main cpc then from MET to gas and water meters and then to the submains db and then from the submains db off to seperate cpc to their own db or the gas and water bonded twice from flats db?