hi guys hope one of you chaps can help.....

I am on a job where we are currently doing 1st fix to five new build flats in stud walls throughout,

The developer and architect have cocked up somewhere and on the plans i have it clearly states that there os 600mm duct for all the submains to main busbar chamber but the ducting very clearly has not been installed. So now we have to pull in the submains through the stud work/joists etc....

I dont see why i need armour cable as now it is not buried and as concealed in the stud walls/floor and will be rccb protected the longest run by the way no more than about 20 metres and all are very small flats no more than 60amps. Please can you lot give more your advice on this as swa it triple the price and job is very tight!

Also what would be the best bonding arrangement i guess a big MET wall mounted and connect to main cpc then from MET to gas and water meters and then to the submains db and then from the submains db off to seperate cpc to their own db or the gas and water bonded twice from flats db?
 
Looks like there going to have to allow for the swa, nightmare if done in t and e on rccb, as when a bulb goes and takes it out likely to be in a locked cupboard tenant can't access.
 
I'd prefer not to rcd the submain, so if something goes in the flat, you don't have to run downstairs to reset it. If the job spec has changed; REJOICE!! you must get paid more for extras??
 
you well have to do your own calcs,but from what you have described I would use 16mm t&e for your subs but run additional cpc .
 
Separate cpc's must be able to carry the full fault current in parallel with the cpc in the cable to be compliant, so there is no real advantage.
 
hi guys hope one of you chaps can help.....

I am on a job where we are currently doing 1st fix to five new build flats in stud walls throughout,

The developer and architect have cocked up somewhere and on the plans i have it clearly states that there os 600mm duct for all the submains to main busbar chamber but the ducting very clearly has not been installed. So now we have to pull in the submains through the stud work/joists etc....

I dont see why i need armour cable as now it is not buried and as concealed in the stud walls/floor and will be rccb protected the longest run by the way no more than about 20 metres and all are very small flats no more than 60amps. Please can you lot give more your advice on this as swa it triple the price and job is very tight!

Also what would be the best bonding arrangement i guess a big MET wall mounted and connect to main cpc then from MET to gas and water meters and then to the submains db and then from the submains db off to seperate cpc to their own db or the gas and water bonded twice from flats db?

Get those who have mucked up top cover the cost of putting it right.
Thus install what ever is needed at their cost NOT yours.
 
thanks guys job is already a bloody night mare! i was thinking to use 16mm t and e with 10mm earths for flat db supplies as its alot cheaper and yh it does state rccb supplies what about bonding arrangement?
 
hi guys hope one of you chaps can help.....

I am on a job where we are currently doing 1st fix to five new build flats in stud walls throughout,

The developer and architect have cocked up somewhere and on the plans i have it clearly states that there os 600mm duct for all the submains to main busbar chamber but the ducting very clearly has not been installed. So now we have to pull in the submains through the stud work/joists etc....

I dont see why i need armour cable as now it is not buried and as concealed in the stud walls/floor and will be rccb protected the longest run by the way no more than about 20 metres and all are very small flats no more than 60amps. Please can you lot give more your advice on this as swa it triple the price and job is very tight!

Also what would be the best bonding arrangement i guess a big MET wall mounted and connect to main cpc then from MET to gas and water meters and then to the submains db and then from the submains db off to seperate cpc to their own db or the gas and water bonded twice from flats db?
you will need armoured subs from the switchroom/ryefield as its within a stud wall (7.2.5)...
 
Am I reading this right? You want to run the submains through the other flats to reach the flat that you need to supply? Then do it in t&e?
 
Each flat should be bonded to their own incoming services at a local earth terminal.

I would use SWA the price is about the same and would avoid needing RCD protection for a submain.
Triple the price sounds wrong somewhere and at about £4/m for 20m the total cost is £80.
(easier to push through holes as well!)
 
hi guys hope one of you chaps can help.....

I am on a job where we are currently doing 1st fix to five new build flats in stud walls throughout,

The developer and architect have cocked up somewhere and on the plans i have it clearly states that there os 600mm duct for all the submains to main busbar chamber but the ducting very clearly has not been installed. So now we have to pull in the submains through the stud work/joists etc....

I dont see why i need armour cable as now it is not buried and as concealed in the stud walls/floor and will be rccb protected the longest run by the way no more than about 20 metres and all are very small flats no more than 60amps. Please can you lot give more your advice on this as swa it triple the price and job is very tight!

Also what would be the best bonding arrangement i guess a big MET wall mounted and connect to main cpc then from MET to gas and water meters and then to the submains db and then from the submains db off to seperate cpc to their own db or the gas and water bonded twice from flats db?


So how is the Water (and Gas if any) service pipes getting to the flats then??

You being serious here, you would seriously use T&E for sub-main cables that pass through other flat's?? ...Jesus!!
 
Don’t know what it is, but anyone with a screen name ****sparky gets my hackles up.

I don’t know about anyone else’s view on it but the word “sparky” brings to mind a cartoon or an unqualified wanabe electrician.

No electrician would be pushed in to making a bodge job as this seems to be.

CGC would turn in his grave!
 