Jun 4, 2020
19
18
33
Hampshire
Hello,
Been to look at job, a barn that's been converted into separate flats. Each one is fed by a 10mm 3C SWA. On peak, off peak and neutral. Currently they just have a double pole main switch for isolation but no protective device. Is there a nice little unit I can use that's designed to deal with something like this? At the moment I thinking of using a 3p&n main switch and then each line on an MCB.
Many Thanks.
10mm supply each? That doesn’t seem very big. Can’t have much in the flats.
How about a 3P MCB ?
In principle, you have a setup that can overload the neutral if both peak & off peak supplies are in use - a 3P MCB will protect against that as well as L-E faults on either supply.
Reactions: PS Electrics
Hello,
Many Thanks.
What's the earthing arrangement. ?
Hello,
Many Thanks.
I take it there's no gas supply obviously but what other main protective bonding conductors are required .
Cheers for the replies.
They are shoe box bedsits, 1 storage heater, immersion, cooker, shower.
It's a TNCS
No gas, no oil, plastic water main.
Thanks, that sounds more tidy than my idea.
It seems crazy the shower will be the same size as main supply but I suppose you could have a 16mm t and e feeding 11 kw shower due to the instalation method ,glass wool ,volt drop etc with a 16mm split con and 80 amp fuse at service head and you would think nothing of it
For prob an extra 50 quid per flat could have went to 16mm .
Hampshire
SWA protection with off peak
Clinchy,
Jock from the north,