Hello,

Been to look at job, a barn that's been converted into separate flats. Each one is fed by a 10mm 3C SWA. On peak, off peak and neutral. Currently they just have a double pole main switch for isolation but no protective device. Is there a nice little unit I can use that's designed to deal with something like this? At the moment I thinking of using a 3p&n main switch and then each line on an MCB.

Many Thanks.
 
10mm supply each? That doesn’t seem very big. Can’t have much in the flats.
 
How about a 3P MCB ?
In principle, you have a setup that can overload the neutral if both peak & off peak supplies are in use - a 3P MCB will protect against that as well as L-E faults on either supply.
 
  • Like
Reactions: PS Electrics
Hello,

Been to look at job, a barn that's been converted into separate flats. Each one is fed by a 10mm 3C SWA. On peak, off peak and neutral. Currently they just have a double pole main switch for isolation but no protective device. Is there a nice little unit I can use that's designed to deal with something like this? At the moment I thinking of using a 3p&n main switch and then each line on an MCB.

Many Thanks.
What's the earthing arrangement. ?
 
Hello,

Been to look at job, a barn that's been converted into separate flats. Each one is fed by a 10mm 3C SWA. On peak, off peak and neutral. Currently they just have a double pole main switch for isolation but no protective device. Is there a nice little unit I can use that's designed to deal with something like this? At the moment I thinking of using a 3p&n main switch and then each line on an MCB.

Many Thanks.
I take it there's no gas supply obviously but what other main protective bonding conductors are required .
 
Cheers for the replies.

They are shoe box bedsits, 1 storage heater, immersion, cooker, shower.

It's a TNCS

No gas, no oil, plastic water main.

How about a 3P MCB ?
In principle, you have a setup that can overload the neutral if both peak & off peak supplies are in use - a 3P MCB will protect against that as well as L-E faults on either supply.
Thanks, that sounds more tidy than my idea.
 
It seems crazy the shower will be the same size as main supply but I suppose you could have a 16mm t and e feeding 11 kw shower due to the instalation method ,glass wool ,volt drop etc with a 16mm split con and 80 amp fuse at service head and you would think nothing of it
 
For prob an extra 50 quid per flat could have went to 16mm .
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Hampshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
SWA protection with off peak
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Clinchy,
Last reply from
Jock from the north,
Replies
7
Views
315

Advert