Hi
I have opened a switch in kitchen to find a loose wire and an upside down switch, the switch powers the main lights, lights under the cupboards and an outside light which I think no longer works.

Just looking see where the loose wire goes and to see if it has been connected properly, the previous owner was had some real funny ideas with the electrics.
 

Attachments

  • 2F92B7E7-E385-43C0-8E38-B51D71F55001.jpeg
    2F92B7E7-E385-43C0-8E38-B51D71F55001.jpeg
    91.7 KB · Views: 33
That is pretty rubbish workmanship, not only has the wire come out but exposed conductor on the other one!

It is most likely going to be one of the two lower holes in the picture. Try one of them, and if the switch operates the wrong way, try the other one instead.

But be very careful to isolate the power, and to be sure you have isolated the actual circuit you are looking at when doing any work!
 
Put it in the one marked "2 way" then it will be the same orientation as the others. They all need reconnecting.
 
That is pretty rubbish workmanship, not only has the wire come out but exposed conductor on the other one!

It is most likely going to be one of the two lower holes in the picture. Try one of them, and if the switch operates the wrong way, try the other one instead.

But be very careful to isolate the power, and to be sure you have isolated the actual circuit you are looking at when doing any work!
When you isolate circuit do you mean turn off lighting switch and then power?
 
Possibly or separate wires in the same terminals. It would appear to be the live feed for the three switches.
 
Turn off the power at the consumer unit by either turning off the circuit breaker or pulling the fuse depending on the age of your installation. If you’re not 100% which device it is turn off the main switch to cut power to the whole house, although I recommend you do this during daylight hours.

If you have some means of testing for dead such as a voltage indicator or multimeter test for voltage between all cables and earth, there shouldn’t be any.

If in doubt STOP.
 
Turn off the power at the consumer unit by either turning off the circuit breaker or pulling the fuse depending on the age of your installation. If you’re not 100% which device it is turn off the main switch to cut power to the whole house, although I recommend you do this during daylight hours.

If you have some means of testing for dead such as a voltage indicator or multimeter test for voltage between all cables and earth, there shouldn’t be any.

If in doubt STOP.
Ok, I always turn all the power off anyway, should there be a sleeve on one of these wires?
 
maybe the loose wire is for the non-working outside light. it could have been dissed due to a fauolt in said light, or it could just have fallen out.
 