LeeH
~
why can't you get a 3core and earth
Because that would make it a 4 core.
And using the third GY core as a phase conductor was my point. You cannot get a suitable 3 core SY for VSD applications for that reason.
why can't you get a 3core and earth
it's an exposed conductive part, therefore it must be earthed.
I am not saying yes or no to earthing it, merely where is the guidance. How are you judging its fault current carrying capabilities.This.
And I think it's nuts saying it does not require it. And I just don't care if it's written in a book or not.
If that cable gets damaged that braid is likely to become live.
I am not saying yes or no to earthing it, merely where is the guidance. How are you judging its fault current carrying capabilities.
I never suggested this, my point being if it is required to carry fault current due to cable damage where is the maths to assess its fault current carrying capabilities.I don't think anyone is using the braided screen as an earth cpc. They are just earthing the screen as its a sensible thing to do.
I never suggested this, my point being if it is required to carry fault current due to cable damage where is the maths to assess its fault current carrying capabilities.
I never suggested this, my point being if it is required to carry fault current due to cable damage where is the maths to assess its fault current carrying capabilities.
Their last para is stark : "We therefore urge extreme caution in accepting the use of YY and SY cable types for UK fixed installations, and to contact the BCA on 0208 946 6978 ..."
I never suggested this, my point being if it is required to carry fault current due to cable damage where is the maths to assess its fault current carrying capabilities.
People are quoting it should be earthed in case the cable gets damaged, say by a nail. What happens when the nail causes a short between a line conductor and the braid, fault current flows. So my point is can the braid carry the fault current and sufficient current without any deterioration of the braid to cause disconnection of the circuit. I am not suggesting its use as a cpc, but if it is earthed there is a possibility it may carry current under fault conditions.It would only need to be assessed for fault current carrying capability if used as a cpc surely ?
When earthed it is connected to cpcs whose capability for fault conditions has already been assessed and verified.
That doesn't even warrant a reply.Do you asses this when earthing cable basket?
No, so I don't see the relevance of its ccc especially as it's not a cpc.