I was asked this many years ago and never got a definitive answer. My opinion is the braid should be earthed but can you give any info as to where this is stated, is it staring me in the face somewhere?
Hi - FWIW I think it should be earthed, too. All I have so far is 131.2.1 "persons and livestock shall be protected against dangers .from. contact with live parts ..." and by earthing the braid it should reduce this risk, I think.
 
Hi - FWIW I think it should be earthed, too. All I have so far is 131.2.1 "persons and livestock shall be protected against dangers .from. contact with live parts ..." and by earthing the braid it should reduce this risk, I think.
The problem I always found it is not recognised by BS7671.
 
Yes, Ruston's post #31 had a link to Eland Cables and I quote them :
"SY control cables are not suitable for fixed wiring applications requiring compliance with the requirements set out in BS7671"
 
Yes, Ruston's post #31 had a link to Eland Cables and I quote them :
"SY control cables are not suitable for fixed wiring applications requiring compliance with the requirements set out in BS7671"
Yeah just looked at that. Must be over 10 years ago I looked into it and gave up, told client I had exhausted all avenues.
 
I would take the approach that the cabling system is live parts in close proximity to a piece of metal that in a fault is almost certain to contact live parts and become live and by the nature of the cable could also be touched at points and would therefore be an exposed conductive part and require earthing.
This avoids all problems about the cable being recognised by BS7671 and just considers the situation in place.
 
I would take the approach that the cabling system is live parts in close proximity to a piece of metal that in a fault is almost certain to contact live parts and become live and by the nature of the cable could also be touched at points and would therefore be an exposed conductive part and require earthing.
This avoids all problems about the cable being recognised by BS7671 and just considers the situation in place.
I totally agree but I have been asked where it says this in black and white in the past. Is it really an exposed conductive part? This is another issue which surrounded the earthing problem.
 
Pigtails are not suitable for EMC compliance, you need to use the correct gland or terminate it into the VSD chassis clamps.

Also the screen should be connected from the VSD chassis back to the motor frame.

Edit: and another thing. Seeing you cannot buy a concentric SY (3 core without a green yellow core) it's not really a suitable VSD cable at all.
Having worked on a VSD today the instructions clearly stated the screen is not to be terminated at the motor but an earth conductor must be provided... What the difference is I have not a scooby doo.

There are 2 earth points between the motor connexions and the VSD cable clamp, and listed for the earth conductor and screen.

Cable being 4 core 6mm² SY.

The reason I was there being a brand new motor (identical make and spec to original) created interference on the BMS in the form of silly 0-10V and 4-20mA readings on nearby sensors... Not an issue with the other motor in the pair or apparently the removed motor.

The only work done being the replacement of 18KW motor by the company maintenance team.

My first check being the 2 worst affected sensor wiring as the maintenance team informed me they had thouroughly checked the motor wiring, both cabled with 0.5mm² SY, plastic cable glanded into BMS enclosure, screen very short pigtailed to earth bar, one sensor in 5 core for 0V, 24Vdc, earth & 0-10V loop. Second being 2 core for 4-20mA. At sensor ends stuffing glanded to sensor, the screens being well isolated. All nicely done and untouched for years.

My next check being the motor wiring, I looked in the VSD first as the cover had been removed; green yellow terminated in one terminal screen pigtailed into other terminal, metal clamp on plastic sheath (only 10mm from earth terminal).
At motor the very brown SY was terminated with new looking brass gland into motor terminal box, the other motor of the pair sported a grey gland which I checked with a meter to be insulating (presumably plastic).
Internally all 4 wires were correctly terminated with new yellow ring crimps onto their studs.

Luckily the brass gland was fitted with locknut and undoing it there was plenty of slack to slide the gland away from the metal enclosure and protecting the wires from chaffing with card the motor was started and ran without altering the sensor readings.

Luckily I had a suitable 25mm stuffing gland and replacing the new brass gland was a fairly easy, maintenance had heatshrink and heat gun to add extra protection to the screen after trimming it back to inside the sheath.

I'd forgotten this thread and found it while looking to see if the subject had been raised here.
 
I’ll find the reference today when I get to not the office, it was 7 years ago though and I don’t have the literature anymore due to a job change. I did extensive research on an interesting job that had some ATEX zones and had a crap load of drives, finding a cable to suit both EMC compliance and ATEX compliance was impossible.

But basically the ideal cable has an external CPC as the twists have a substantial effect. The 4th core inhibits this.

Using the EMC clamp on the insulation and pig tailing the braid is a bit dumb though.

Anyway, I used SWA in the end and rode off into the sunset on my horse as the perfect cable does not exists and I couldn’t bring myself to use flexible cables in that environment.
 
Last edited:
@sunray An edited snippet below regarding grounding at one end and the use of pigtails.

This requirement to employ ‘good EMC
engineering practices having regard to
the state of the art’, is a big problem for

electrical engineers, etc., since most
of them seem to believe that all that is
required for good EMC engineering is to
use single-point earthing (grounding)
terminate cable shields at one end only,

These might possibly have been
acceptable EMC practices in the 1950s,
when FM Radio and Television at VHF
were new and considered to be the
pinnacle of high technology, and digital
circuits and software were not even on
the horizon. But they are generally bad
EMC engineering practices these days

Remember that pigtailed shields are
never going to be much use for EMC




Also cable suggestions form the ATV930 drive manuals that we used. So its the core symmetry, not the twists. Bit instrumental cables have twisted pairs for this reason.

1681139360611.png
 
Last edited:

Reply to SY, CY None Compliant???? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hello 1. When taking R1+R2 readings on the AM2 composite installation are we expected to take the reading at the supply side of the FCU (S-plan &...
Replies
17
Views
5K
Hi, Sorry If I am posting in the wrong place, I am new. If you could take the time to read my post, I would appreciate it more than you know. I...
Replies
6
Views
2K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock