understand completely Guitarist, i am refering to post no.9 .When using a 1361 fuse in a FCU to protect the fan.As post no.9 refers to a 60898 mcb tripping sooner ???????? would have thought 3amp 1361 should have blown first but not sure where i can confirm this,telectrix prob. right ??? confused
 
interesting post telectrix , so it begs to answer the previous posts of someone being prosecuted that did not put in a 3amp fuse.Fan caused a fire as it was not fused at 3amp!!! as you say discrimination (or new 17th term selectivity i think!)wise the 60898 would trip first,so a 3amp would have made no difference?.Just for legal clarity could you give me the page no./ time characteristics on bs 7671 for the 60898 and also for the 1362 fuse if thats what i believe the crux of the issue is about.Thanks
BS EN 60898 BGB Page 301
BS 1362 not in BGB see link Note. curves shown are 1A and 13A, you will need to interpolate for 3A - http://www.farnell.com/datasheets/10867.pdf

 
Last edited by a moderator:
From what I can gather in this situation..

6A MCB will trip within 0.1 secs at 30A
3A BS1362 fuse will blow at a max of 8x its rated current in 0.1 secs (24A)........ 3A fuse safer

6A MCB will trip within 100 secs at 14A
3A BS1362 fuse will blow at 6.3A max.................3A fuse safer


I would conclude that across the board, the 3A fuse is indeed the better OCPD in this instance.

Please feel free to correct me in this. I am very interested to see if I have interpreted the graphs incorrectly.
 
Anyone ever have a fuse or a mcb actually disconnect a domestic fan ?

My own feeling is neither will go,the fan windings will cough up the proverbial before either of them get their act together

With my reasoning in mind,the cheap and nasty fans will no doubt be safer than the quality jobs,so good protection can be achieved by purchasing down market gear :biggrin5:
 
On a well maintained fan I can't see too many problems when the fan packs up, the problem occurs when there's 30 years of crap in there that tends to catch fire. Seen countless fans that look like the vacuum cleaners been emptied into them, such a delight to clean.
 