Discuss Tables for SWA armour cpc? in the UK Electrical Forum area at ElectriciansForums.net
Rockingit
Mentor
Supporter
In a former life on another forum as well as this one.... there were a whole heap of downloads that people had done as ready-reckoners for things like Cu eq for various armour sizes, R1R2 values on lengths.. useful stuff. I think I might even have generated some myself.
Anyone have any still??! A dig around in my own archives isn't turning up much.
Try the OSG
Are those you are after...
Cheers both. I vaguely recall that I did a spreadsheet which then included the steel to copper maths as well but both these are kinda what I was after. I really must get around to ordering a copy of GN8!
Hello Rockingit. It's Table D9 for 70 deg C and D10a for 90 deg C in IET Guidance Note 1.
Regards,
Colin Jenkins.
Reply to Tables for SWA armour cpc? in the UK Electrical Forum area at ElectriciansForums.net
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
I want to use the armour as my CPC but need to check it complies. The cable will be run from a SP Distribution panel to CU. As per Selection and...
6K
Octopus
O
As you may know looking at some of my posts I've been thrown back in the deep end recently – and don’t have much experience with complicated...
4K
B
I'm doing a mod for a 3 phase circuit already installed. The only trouble is I can't work out why the existing cables are as they are so i am...
6K
C
Something I haven't really done, so am I correct with the Maths? Just looking to reduce costs & use 2 core against 3. Found the Table from the...
10K